Hi all, went to a job today to price up an shower install, it was a TT so as i was leaving i decided to do a quick check on the main earthing conductor as i could not see earth rod pit outside house, i had a look inside db and could only see 2 x 10mm earths which i assumed are gas/water.
Quickly isolated installation and went across earth bar and incoming L/N and did Ze got 102.4 ohms, it had a 30mA rcd incomer, could not see a main earth as it was only a quote did not want to get too involved, also did an RCD auto test, all the times were fine and did a Zs at a socket under DB and got reading of 105 ohms.
I am 99% sure there is no earthing conductor, is the RCD adequate? the way i see this if the RCD fails there is no means of fault protection, gonna check the regs in a bit but wanted some second opinions
Quickly isolated installation and went across earth bar and incoming L/N and did Ze got 102.4 ohms, it had a 30mA rcd incomer, could not see a main earth as it was only a quote did not want to get too involved, also did an RCD auto test, all the times were fine and did a Zs at a socket under DB and got reading of 105 ohms.