so currently doing my level 3 diploma and have this question I'm stuck on can anyone help?

a radial circuit is protected by 20A type B circuit breaker and is wired using 2.5mm2 70C thermoplastic single core live conductors with 1.5mm CPC to a length of 28mm in steel trunking. ambient temp is 20C supply is 230V single phase TNCS system. Ze & prospective fault current is recorded at 0.1 ohms and 2.3KA.

- already worded out R1 and R2 for the circuit which is 0.546.
- NEED to find - value of short circuit at end point of the circuit?
- AND will the circuit breaker disconnect within the required time under fault conditions.?

Cheers
 
You have Ze and you have R1+R2
Ipf at the end of the circuit (not normally considered in calculation) is Uo/Zs.
Zs = Ze+(R1+R2)
Zs at ambient temperature may corrected to Zs at Line maximum permitted operating temperature by dividing by 0.8.
Alternatively maximum Zs for a 20A circuit breaker to BSEN60898 as given in table 41.3 in BS7671 can be corrected to ambient temperature by multiplying by 0.8 (chapter 14 BS7671), this will give you the values of Zs as given in the on site guide.

So long as the Zs for the circuit is less than the tabulated values for a 20A BSEN60898 then the circuit breaker will disconnect in the required time.

View attachment 35140
 
as i read the OP, it's a radial circuit 28m long. so that's 28m from origin to load. maybe you were thinking of a RFC?
 
You have Ze and you have R1+R2
Ipf at the end of the circuit (not normally considered in calculation) is Uo/Zs.
Zs = Ze+(R1+R2)
Zs at ambient temperature may corrected to Zs at Line maximum permitted operating temperature by dividing by 0.8.
Alternatively maximum Zs for a 20A circuit breaker to BSEN60898 as given in table 41.3 in BS7671 can be corrected to ambient temperature by multiplying by 0.8 (chapter 14 BS7671), this will give you the values of Zs as given in the on site guide.

So long as the Zs for the circuit is less than the tabulated values for a 20A BSEN60898 then the circuit breaker will disconnect in the required time.

View attachment 35140

Thanks Richard this really helped
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Can someone help?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
Phil Griffiths,
Last reply from
Phil Griffiths,
Replies
21
Views
4,583

Advert

TrueNAS JBOD Storage Server

Back
Top