so currently doing my level 3 diploma and have this question I'm stuck on can anyone help?

a radial circuit is protected by 20A type B circuit breaker and is wired using 2.5mm2 70C thermoplastic single core live conductors with 1.5mm CPC to a length of 28mm in steel trunking. ambient temp is 20C supply is 230V single phase TNCS system. Ze & prospective fault current is recorded at 0.1 ohms and 2.3KA.

- already worded out R1 and R2 for the circuit which is 0.546.
- NEED to find - value of short circuit at end point of the circuit?
- AND will the circuit breaker disconnect within the required time under fault conditions.?

Cheers
 
You have Ze and you have R1+R2
Ipf at the end of the circuit (not normally considered in calculation) is Uo/Zs.
Zs = Ze+(R1+R2)
Zs at ambient temperature may corrected to Zs at Line maximum permitted operating temperature by dividing by 0.8.
Alternatively maximum Zs for a 20A circuit breaker to BSEN60898 as given in table 41.3 in BS7671 can be corrected to ambient temperature by multiplying by 0.8 (chapter 14 BS7671), this will give you the values of Zs as given in the on site guide.

So long as the Zs for the circuit is less than the tabulated values for a 20A BSEN60898 then the circuit breaker will disconnect in the required time.

View attachment 35140
 
You have Ze and you have R1+R2
Ipf at the end of the circuit (not normally considered in calculation) is Uo/Zs.
Zs = Ze+(R1+R2)
Zs at ambient temperature may corrected to Zs at Line maximum permitted operating temperature by dividing by 0.8.
Alternatively maximum Zs for a 20A circuit breaker to BSEN60898 as given in table 41.3 in BS7671 can be corrected to ambient temperature by multiplying by 0.8 (chapter 14 BS7671), this will give you the values of Zs as given in the on site guide.

So long as the Zs for the circuit is less than the tabulated values for a 20A BSEN60898 then the circuit breaker will disconnect in the required time.

View attachment 35140

Thanks Richard this really helped
 

Reply to Can someone help? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
962

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top