Can we use the armour of an SWA as the CPC??? | Page 11 | on ElectriciansForums

Discuss Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Unless you are installing big boy cables where the armour isn't sufficient, why waste money on an extra core for the earth when you've got a perfectly good enough one in the armour, assuming one buries it correctly (no potential sheath damage)
 
I agree. Using the armour is the way to go but my point related more to the suggestion of attaching a separate CPC on the outside which in my humble opinion is a little pointless. Why have SWA if you going to compromise on the protection of the CPC?
 
I agree. Using the armour is the way to go but my point related more to the suggestion of attaching a separate CPC on the outside which in my humble opinion is a little pointless. Why have SWA if you going to compromise on the protection of the CPC?

The armouring prevents the live conductors from getting damaged etc. even if the cable was crushed it would just short to earth, hence no shock risk. Therefore the earth even if it was squashed wouldn't shock anyone.
Even if you repeatedly drove over a 25mm single cable, you would probably only damage the insulation, not the copper.
 
If you even thinking of possible damage to armouring on a SWA cable install a 3 Core for 1 Phase installs and
a 5 core for 3PH installs... Life is more important than money ....Labour costs etc etc on installing seperate earthing. IHMO
 
Here is an updated table that i have been using for several years now on SWA compliance, for using the armour as your CPC

Figures in brackets, ... DO NOT COMPLY.



Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.


Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
15
16
17
2.5
5.7
17
19
20
4
9.0
21
23
35
6
13.6
24
36
40
10
22.6
41
44
49
16
36.1
46
50
72
25
36.1
60
66
76
35
36.1
66
74
84
50
56.4
74
84
122
70
79.0
84
119
138
95
107.2
122
138
160
120
135.3
(131)
150
220
150
169.2
(144)
211
240
185
208.6
(201)
230
265
240
270.6
(225)
(260)
299
300
338.3
(250)
(289)
(333)
400
403.9
(279)
(319)
467


Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.


Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
16
17
18
2.5
5.7
17
19
20
4
9.0
19
21
23
6
13.6
22
23
36
10
22.6
26
39
43
16
36.1
41
44
49
25
36.1
42
62
70
35
36.1
62
70
80
50
56.4
68
78
90
70
79.0
80
90
131
95
107.2
113
128
147
120
135.3
(125)
141
206
150
169.2
(138)
201
230
185
208.6
(191)
220
255
240
270.6
(215)
(250)
289
300
338.3
(235)
(269)
(319)
400
451.0
(265)
(304)
452
 
In addition to that:
Steel wire armoured cable, commonly abbreviated as SWA, is a hard-wearing power cable designed for the supply of mains electricity. It is one of a number of armoured electrical cables – which include 11kV Cable and 33kV Cable – and is found in underground systems, power networks and cable ducting. Steel wire armour is only used on multicore versions of the cable. A multicore cable, as the name suggests, is one where there are a number of different cores. When SWA cable has only one core, aluminium wire armour (AWA) is used instead of steel wire.
 
Here is an updated table that i have been using for several years now on SWA compliance, for using the armour as your CPC

Figures in brackets, ... DO NOT COMPLY.



Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.



Conductor CSA

Minimum CSA of SWA to meet 54G

CSA of armour 2 core

CSA of armour 3 core

CSA of armour 4 core

1.5

3.4

15

16

17

2.5

5.7

17

19

20

4

9.0

21

23

35

6

13.6

24

36

40

10

22.6

41

44

49

16

36.1

46

50

72

25

36.1

60

66

76

35

36.1

66

74

84

50

56.4

74

84

122

70

79.0

84

119

138

95

107.2

122

138

160

120

135.3

(131)

150

220

150

169.2

(144)

211

240

185

208.6

(201)

230

265

240

270.6

(225)

(260)

299

300

338.3

(250)

(289)

(333)

400

403.9

(279)

(319)

467


Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.



Conductor CSA

Minimum CSA of SWA to meet 54G

CSA of armour 2 core

CSA of armour 3 core

CSA of armour 4 core

1.5

3.4

16

17

18

2.5

5.7

17

19

20

4

9.0

19

21

23

6

13.6

22

23

36

10

22.6

26

39

43

16

36.1

41

44

49

25

36.1

42

62

70

35

36.1

62

70

80

50

56.4

68

78

90

70

79.0

80

90

131

95

107.2

113

128

147

120

135.3

(125)

141

206

150

169.2

(138)

201

230

185

208.6

(191)

220

255

240

270.6

(215)

(250)

289

300

338.3

(235)

(269)

(319)

400

451.0

(265)

(304)

452

can i just add, that they do not comply with table 54G, but may comply by calculation, using the adiabatic. I seem to remember that the only size that doesnt comply with the adiabatic is 400mm2 2c. This will need you to verify this though, dont take my word for it.
 
I have a job coming up in the school hols to supply 2 temporary portacabin type classrooms which will be set up as technology workshops untill xmas. 60amp 60898 3 phase protective device. It's a 150m run which means that due to volt drop I'll have to use 50mm SWA. Now I'd like to use 5core and include an integral cpc but theres about ÂŁ1200 difference between 4 and 5 core so thats out. I could run a seperate earth if I specially ordered 150m of 25mm which would be better value but is it necassary? From the previously listed tables it's not but as it's a school I'd like to have 'belt and braces'
So my question is, who would run a seperate cpc and who wouldn't?

It'll probably be nicked by pikeys in 10 minutes anyway, they had 100m x 6m of lead off a roof at the same school last year...
 
Can I ask Tonka first off why the 60amp load, will that be for heating these cabins?

I'm assuming that your taking the VD from the In rather than the Ib ?

Why the 5 core is it a 3phase supply?

Are you going to be classing these as a temporary structure and therefore under section 717. I would think they should be and therefore if you have a PME system you need to make sure you can export it as per reg 717.411.4, which should be ok, just want to make you aware of it.

Personally that long a run I would be looking very closely at the design load, to try and use a smallish cable as possible, especially as it is temporary. I certainly would not be looking at running a separate CPC for it . Is there no design criteria for this by the customer or their representative
 
can i just add, that they do not comply with table 54G, but may comply by calculation, using the adiabatic. I seem to remember that the only size that doesnt comply with the adiabatic is 400mm2 2c. This will need you to verify this though, dont take my word for it.

Using the table i re-posted above (post 155) (originally posted by Spinlondon) and i can assure you, ...you won't go far wrong. There is no need for any further calculation to the above complying cables...
 
I've been dropped in at the deep end really. Story is: 2x tech workshops burnt out due to unknown cause a couple of months ago, whilst the workshops are refurbished the classes need to go ahead and they've decided to have 2 portacabin type classrooms delivered to a hard standing about 100 meters away as the crow flies. They can't tell me the exact load they will be using, only that each cabin will have 2x 3phase machine circuits. (lathes or pillar drill I expect) a couple of pc work stations, sockets, lights and more than likely heating as they will be up until at least xmas. The sockets will be used by classes using basic tools inc a rack of heat guns, vac pac machines etc. Quite a load if 5 or 6 kids all have heat guns on the go.
I'm going to use the 60amp MCB originally used to supply one of the burnt out classrooms which originally had 5-8 3phase machines in. (con unit well away from fire thankfully)
In used as they can't tell me at the moment exactly what Ib is and I suspect it will creep up and up as they find more machines to runs and it gets colder.

We do all the maintenance and smaller works at the school but installing an IT suite or installing a new 16amp welder socket is a far cry from this.

Thinking some more, it may be more cost effective to come from the existing 60amp mcb (can't change it for a different MCB as its about a 50 years old and no longer availible) to a standalone 32amp switch fuse, then use a much smaller cable? I'd rather do that as I can't believe 150m of 50mm 4core will be very easy to work with
Thanks for your help.
 
Last edited:
So are you going to give each cabin 30amps of 3 phase supply ( You said your main breaker was 60amp I assume 3 phase 60amp)

So if the cable works out at 50mm and is the most expensive part of the install, then why don't you fit 2 x 32amp 3 phase breakers under the existing 60amp one, and run 2 X 3 phase 32amp supplies out, you most likely would get away with 16mm and possibly 10mm if you had a better idea of your loads
 
So are you going to give each cabin 30amps of 3 phase supply ( You said your main breaker was 60amp I assume 3 phase 60amp)

So if the cable works out at 50mm and is the most expensive part of the install, then why don't you fit 2 x 32amp 3 phase breakers under the existing 60amp one, and run 2 X 3 phase 32amp supplies out, you most likely would get away with 16mm and possibly 10mm if you had a better idea of your loads

Ok, that sounds like a winner, I'll get my head back in the books and work out sizes based on 2 32amp instead of 1 60amp. It'll also have the advantage of the rennovation sparkies having the option to supply the 2x32a board from a different place if they need to rip out the existing con unit as part of their work.

I'm going to take a guess at the proposed load per cabin.
2x 3phase lathes or pillar drills
6x 5' flurescents
1x pc workstation
various low powered hand tools. ie, soldering irons.
5x heat guns that may concievably be used at the same time.
2x 2kw convectors when it gets colder.
1x 13amp plastic former

Cable run is through ceiling void to outside, no applicable grouping, thermals or insulation. Clipped direct on wall, 3m duct under steps, clipped direct to fence, 1m duct under gateway, grouped with 32amp single phase swa along fence to cabins.
What size(s) would you go for?
 
Last edited:
Well mate you have a 3 phase supply so you put the 2 heaters on a phase each so there is 8/9 amps there you have a couple of smallish 3 phase lathes/ drilling machines so what would you say 9/12 amps spread over your 3 phases that make 3/4 per phase so your worse case will be 15amps per phase.

The rest of the load will go on the other phase lights, smallish hand tools etc, former so you may have a load of 15/17 amps per phase.

You could get away with 10mm especially if your being generous and the run is less that the 150 you think it is.
 

Reply to Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
419
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
yes it was a pee-take... I was commenting if someone was dumb enough to use earth clamps on armour, they might just be dumb enough to earth a...
Replies
6
Views
513

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top