Yes, Spinlondon is right, ridiculous contradictions between BS7671 and Guidance Note 8.

The original reason for the reg was to nul circulating currents, following it to the letter would preclude the use of conventional pvc/pvc switch drops where the neutral would not be present.
 
I think you are both reading to much into this.
Running a separate earth is an industry wide practice that has been in use for generations. The reg you're quoting is written for single swa cable & ferromagnetic enclosures. This reminds me of the 15th edition when it came out and everyone bonding any piece of metal in the home.

As regards a switch drop, a length of conduit with a live & switch live in it has no current flowing through it in normal circumstances so there would not be a problem.
 
Andy, don't think that I'm saying 'don't run a separate cpc with swa' that's not the case, I'm merely agreeing with Spinlondon on the interpretation.
 
I know IQ, as I said it's not clear. I just think that in this instance the IEE are not meaning the armoure as an enclosure as stated. Which is why they say single armoured cable & ferromagnetic enclosures. Otherwise they would not say single core armoured, as it would apply to all armoured.
(if that makes sense)
 
I know IQ, as I said it's not clear. I just think that in this instance the IEE are not meaning the armoure as an enclosure as stated. Which is why they say single armoured cable & ferromagnetic enclosures. Otherwise they would not say single core armoured, as it would apply to all armoured.
(if that makes sense)
This Regulation is aimed at mitigating the effects that are caused by unwanted magnetic fields (eddy currents).
They did not include multicore SWA cables in with the single core SWA cables, simply because multicore SWA cables are acceptable for a.c. circuits.
It is quite obvious that SWA is considered to cause unwanted magnetic fields, otherwise there would be no constraints against using the single core SWA cables.
They haven't specifically mentioned multicore SWA cables, just as they haven't specifically mentioned galvonised steel conduit, galvonised steel trunking or even maleable iron conduit as all of these are covered by the term 'ferromagnetic enclosure'.
Now you have stated that the practice of running a separate earth has been in use for generations.
Are you sure that it has been for that long, and do you know whether the separate earth is a CPC, or a bonding conductor?
The armour while acceptable for a CPC, is not acceptable for bonding, as such a separate conductor is required.
 
This Regulation is aimed at mitigating the effects that are caused by unwanted magnetic fields (eddy currents).
They did not include multicore SWA cables in with the single core SWA cables, simply because multicore SWA cables are acceptable for a.c. circuits.
It is quite obvious that SWA is considered to cause unwanted magnetic fields, otherwise there would be no constraints against using the single core SWA cables.
They haven't specifically mentioned multicore SWA cables, just as they haven't specifically mentioned galvonised steel conduit, galvonised steel trunking or even maleable iron conduit as all of these are covered by the term 'ferromagnetic enclosure'.
Now you have stated that the practice of running a separate earth has been in use for generations.
Are you sure that it has been for that long, and do you know whether the separate earth is a CPC, or a bonding conductor?
The armour while acceptable for a CPC, is not acceptable for bonding, as such a separate conductor is required.

I think you have basically said the same as me other than your last line.
Where does it say that you can't use the armour as a bonding conductor.
I've always thought that (assuming all the calcs allow) you can use the armour- as a cpc, bonding conductor, earth conductor or indeed all these at once.
In other words, if you were running a sub main you could use the armour as a combined cpc and bonding conductor.
 
Sorry that statement was in relation to TN-C-S systems and yes technically you could size an SWA cable to allow the armour to be acceptable as a bonding conductor.
However the practicalities would preclude it. To meet the requirements of Table 54.8 the armoured cable would have to have conductors at least twice the size of the supply neutral.
As such if your supply neutral is anything up to 35mm² which would require a 10mm² bonding conductor, your SWA cable would have to be 70mm² for the armour to have a 10mm² copper equivalance.
I wouldn't be able to justify using a 2 core 70mm² SWA cable instead of a 2 core 6mm² SWA cable with separate 10mm² bonding conductor
 
Last edited by a moderator:
Sorry spinlondon but I'm lost now.
I don't understand where you are getting 70mm from.
10mm 2 core pvc/swa cable has a armour equivalent of 17.7mm copper. Going by earthing nuts chart.
 
The ratio for electrical conductivity between copper and steel is about 8 or 9:1, depending on the make up of the materials.
The chart you are refering to probablly relates to the thermal resistivity.
 
Last edited by a moderator:
Sorry that statement was in relation to TN-C-S systems and yes technically you could size an SWA cable to allow the armour to be acceptable as a bonding conductor.
However the practicalities would preclude it. To meet the requirements of Table 54.8 the armoured cable would have to have conductors at least twice the size of the supply neutral.
As such if your supply neutral is anything up to 35mm² which would require a 10mm² bonding conductor, your SWA cable would have to be 70mm² for the armour to have a 10mm² copper equivalance.
I wouldn't be able to justify using a 2 core 70mm² SWA cable instead of a 2 core 6mm² SWA cable with separate 10mm² bonding conductor

You have lost me too.....

if you use the adiabatic regarding a 35mm 4c for say a TP+N PME supply then the armouring has a resistance of 2 miliohms/metre, coupled with a CSA of 70mm.. i bet you find the armour is more than adequate....

have you read my previous post in this thread? its just your calcs dont seem to add up.... you dont need to consider ratios of conductivity between steel and copper when you know the resistance of the armour and you have the other info required to make the calc.....
 
35mm 4 core to bs 6346 is just about adequate for a 10mm bond
conductivity of copper is about 8 x more than swa
(pme only)

BS 6346? not familiar with that. generally use cable to 5467 or 6724.

plus i dont see your point... copper is a great conductor, but as previously mentioned to follow regs use table 54.7 or use the adiabatic.... How can you say that cable is suitable when you havent stated it length, a Zs value etc...... every scenario is different....
 
Last edited:
(pme only & bonding conductor )
35mm four core swa to bs 5467 is just about adequate for a 10mm bond
min size of swa which would equal a 10mm bonding conductor in copper

swa just cpc use adiabatic...
 
Last edited by a moderator:

Reply to Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
703

Similar threads

totally agree
Replies
12
Views
1K
yes it was a pee-take... I was commenting if someone was dumb enough to use earth clamps on armour, they might just be dumb enough to earth a...
Replies
6
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top