I have seen numerous times what happens to the armour when the sheath of the cable is damaged, and water starts to ingress.
The ratio for electrical conductivity between copper and steel is about 8 or 9:1, depending on the make up of the materials.
The chart you are refering to probablly relates to the thermal resistivity.
Hello again sparkies, here is a snippet of my project submitted for 2391-20 qualification regarding minimum size of S= √(1966²×0.1)/46=13.5mm²
Using the table provided by AEI I can see that a 70mm² four core cable has a 131mm² armour CSA, therefore this is perfectly acceptable.
[/I]
This shows that the armouring can handle 10x the amount of fault current that is required....!! no need for seperate CPC ;-)
Please note: values for armour and conductor resistance are from AEI cables, vvv useful!!! as you dont find them in the regs book, OSG etc. (OSG up to 50mm and doesnt show armour resistance.... there is a way of calculating conductor resistance but i cant remember how.....
Was going to post link to AEI site but you need to be a member to view the datasheets.... if anyone wants to see them and needs assistance then let me know
hope this helps AMP DAVID!!!
It would depend on what it is you wish to achive.
If for instance you wish to determine whether the armour of an SWA cable is suficient to be used as a CPC, then I would either use the cable manufacturer's data or perhaps a chart that you feel is reliable, and then apply the adiabatic equation.
If however you wished to determine, whether the armour was suitable to be used as a bonding conductor, I probablly wouldn't bother making the attempt other than as an exercise to prove to someone that the armour is not sufficient.
Just throwing this in because i'm sick of reading these threads about very basic electrical practise. If you have to ask questions like this then you shouldn't be touching any electrical installation above a 13amp plug!!!