Hi, my question is. If I have an old wylex consumer unit with NB type 2 breakers (not 60898). Or let's say any CU for that matter. If it's protected by a 30ma RCD, will that pass the cert?. Or for example will the use of old mcbs not be up to standard. Thanks
 
The installation needs to be in a safe condition to extend.
Any new circuits or alterations need to meet latest regulations.
It's theoretically possible to comply using a rewireable board.

Numerous questions come to mind, for for starters:
Where is the RCD installed, between meter tails and consumer unit, or at the start of the new circuit?
Has a surge protection device been installed?
Is the lighting in the extension RCD protected?
Is there a bath or shower room in the new extension?
 
No, new ring has been wired to a new extension at the back of the house and just needs an EIC.

The installation needs to be in a safe condition to extend.
Any new circuits or alterations need to meet latest regulations.
It's theoretically possible to comply using a rewireable board.

Numerous questions come to mind, for for starters:
Where is the RCD installed, between meter tails and consumer unit, or at the start of the new circuit?
Has a surge protection device been installed?
Is the lighting in the extension RCD protected?
Is there a bath or shower room in the new extension?
 
Thanks for the reply This is the puppy, RCD protecting all circuits in the house. Everything past this consumer unit meets regs. If RCD is testing fine and all other tests are fine. Would this be acceptable to sign off, or would most go down the consumer unit change route?
 

Attachments

  • [ElectriciansForums.net] Can you sign off any work with a 30ma RCD.
    Screenshot_2022-07-23-21-54-40-74_99c04817c0de5652397fc8b56c3b3817.jpg
    86 KB · Views: 47
In general I can't see why under amendment 1 this couldn't be extended. There's a reg recommending dividing the installation to avoid nuisance tripping.
Pragmatically, the RCD is very old and I wouldn't trust it too much. Is this a TT installation?
There's a few reasons I'd rather not, but I don't think I'd be prevented from doing so.

From September (Amendment 2) there would need to be a statement saying no SPD is required, and I'd not be adding a sockets circuit protected by a type AC RCD.
 
In general I can't see why under amendment 1 this couldn't be extended. There's a reg recommending dividing the installation to avoid nuisance tripping.
Pragmatically, the RCD is very old and I wouldn't trust it too much. Is this a TT installation?
There's a few reasons I'd rather not, but I don't think I'd be prevented from doing so.

From September (Amendment 2) there would need to be a statement saying no SPD is required, and I'd not be adding a sockets circuit protected by a type AC RCD.
Thanks for the info. It's a tncs
 
Ok, so it's a PME supply.

Are the meter tails 25mm and is the earthing conductor 16mm?
Bonding conductors 10mm?

Plastic CU is not an issue unless thermal damage is noticed.

There's also the question of maximum demand of 63A at the RCD being exceeded here.

Lighting - 66% of total current demand for each circuit
Power - 100% of the first ring circuit + 40% of all other circuits
Cooker - 10A + 30% of remaining rated current + 5% if the CCU has a socket outlet
Shower - No diversity allowable
Instantaneous water heater - 100% of largest heater + 100% of second largest + 25% of of any others
Thermostatically controlled water heater - No diversity allowable
Underfloor heating - No diversity allowable

Does the test button on the RCD function ok?
Does the RCD trip within 40ms on a 5x test?
Does the EFLI of each circuit measure below the max zs?
Clearly IR is good on each circuit as you would have nuisance tripping otherwise.

At the end of the day, it is irrelevant what the customer wants. You are the qualified & competent person carrying out the inspection and it's your professional opinion that matters here.

Ultimately, is the electrical installation safe for continued use?

You can run yourself in circles questioning yourself with EICR's.
Take a step back, look at the installation as whole and make a professional judgement based on what you see.
 
There's the non-combustible consumer unit question too.
You don't have to change a plastic CU to install a new circuit, though.

It's not ideal but I feel that if the new installation meets regulation standards it would be OK...as long as the existing installation supply requirements are also up to standard.
Plenty of questions need answering, as you say.
 
Last edited:

Reply to Can you sign off any work with a 30ma RCD. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
638
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top