HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,278
Reaction score
6,522
Location
Gloucestershire
Evening chaps..

I have just fitted some downlights in a bathroom and needed to give them RCD protection as there was none. I fitted the following:

[ElectriciansForums.net] Cannot get RCD test to work?

The test button works fine and the unit trips when a fault occurs (touching neutral to earth) but I cannot get the MFT to test it for trip times which I need for the MWC. Its a fairy decent MFT and I've never had any trouble with it testing RCD's before but I have never tested this sort of RCD before, it has always been in the CU. I make contact with the live/neutral/earth of something which the RCD is feeding, I get the little 'tick' on the MFT and then it just wont test.

Am I missing something simple here? Is this unit tested in the same way as you would an RCD in a CU?
 
may just not test at all....

personally i think theres either a lack of understanding about how to carry out the test competantly from the OP (hardly surprising)

or theres no continuity of CPC someware......

if theres any exposed pipework nearby the OP could prove the no continuity of CPC easily by connecting the earth croc to extranious whilst testing the RCD.....if it lets go then i would dare say its a CPC thing....

Back to your old ways then Glenn.. for a brief moment I thought it looked like you were becoming an adult.

Bit exhausting to keep saying it, so I'll give up after this... but have another read of the thread.
 
have you not considered that you may have disturbed the CPC someware....probably whilst trying to put fronts on..

and it would be refreshing if you actually took on board some of the advice given as well (from me & others)...this would include the bottom sentance at #73...

rather that being....somewhat selective with your highlighting.....

just a thought mind you....take it or leave it...
 
Yes definatly, I reckon it is that, but it would seem that many would just rather assume that OP cannot test correctly.
well come on...

what are we supposed to think when he comes in asking how to wire up a bloody bell

or how about the classic fail that was the dis-board change without any pre-testing...anyone remember that one?

oh and by the way before you decide to start...i`m not on my own in regard to this either....

i said before that the OP would be better shadowing an experienced electrician for at least a year before carrying out any more work on his own...

i still stick by this....
 

Reply to Cannot get RCD test to work? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
378
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
625

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top