Can't see supplementary bonding in bathroom | on ElectriciansForums

Discuss Can't see supplementary bonding in bathroom in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

silure130

Hi
What happens when you guys are testing and you can't see if there is any supplementary bonding in the bathroom, and cannot see the clamps on any pipe work.

The shower is rcd protected but the lighting is not. Would you code it C2 for the bonding and C3 for the lighting not being on the RCD.

Would then fitting a RCBO for the lights or moving them to the the RCD side of the board meet the requirements.

My line of work is industrial, motors, plcs etc. I'm starting to get interested in the testing side and have a few books, the above scenario is my own bathroom so I'm using it as a bit of a practice.

thanks
 
Hi
What happens when you guys are testing and you can't see if there is any supplementary bonding in the bathroom, and cannot see the clamps on any pipe work.
It could be elsewhere.
Are the parts extraneous?
Measurements need to be taken.

The shower is rcd protected but the lighting is not. Would you code it C2 for the bonding and C3 for the lighting not being on the RCD.
That depends which, if anything is wrong or missing.

Would then fitting a RCBO for the lights or moving them to the the RCD side of the board meet the requirements.
It could but may it not be necessary.



You need to test to determine if supplementary bonding is required.
 
Thanks for the reply.
There is definately no connections elsewhere. I've looked in the airing cupboard which is next to the bathroom.
Extraneous parts, are these the copper pipes coming into the bathroom. The whole house is copper, no plastic anywhere.

"You need to test to determine if supplementary bonding is required. "

This is the bit im not sure on. I'm thinking its maybe to late in life for me to start trying to get my head around this because I'm usualy pretty good but I cant grasp this.

ta



It could be elsewhere.
Are the parts extraneous?
Measurements need to be taken.


That depends which, if anything is wrong or missing.


It could but may it not be necessary.



You need to test to determine if supplementary bonding is required.
 
Main Protective Bonding must be correct.

Supplementary bonding in the bathroom is applied to extraneous-conductive-parts and exposed-conductive-parts to reduce the potential difference between them to a level that is deemed safe in fault conditions - 50V.

To determine this, firstly, measure the resistance between all parts which may be extraneous and the Main Earthing Terminal.
If greater than 23kΩ (some prefer 46kΩ) then the part is considered not extraneous and no supplementary bonding is required.

Next, measure the resistance between all the parts which are extraneous and between these parts and the CPCs of the circuits in the bathroom.
If less than 50V/Ia then supplementary bonding is not required.
Ia being that for the highest rated OPD of the circuits in the bathroom.

If, for example, there is only a 6A lighting circuit in the bathroom then resistances between parts can be less than 50/30, that is 1.66Ω
Only above that is supplementary bonding required.
With a 40A shower circuit in the bathroom the figure is 50/200, i.e. 0.25Ω.

RCDs on ALL the circuits can with other criteria allow supplementary bonding to be omitted altogether.


So depending on your situation supplementary bonding may or may not be required.
You cannot tell by looking.

As you say yours is all copper it is likely that the pipes will be extraneous but very short runs may be of low enough impedance that no supplementary bonding is needed.



Edit - figures are for B type MCBs.
 
Last edited by a moderator:
Me and Geoff have smashed out supplementary bonding debates on many occasions! I can't think of anyone more suitable to explain it in such an effective yet simple way :)
 
I'm afraid I tend to think with how bonding has changed over the years too many find it hard to understand, that it either gets missed out or bonded when not required, in a way bonding all pipes in bathrooms required or not used to ensure everything was covered, but money seems to be the driving force now.
 
Thanks very much Geoff, I appreciate you taking the time to explain it.


Main Protective Bonding must be correct.

Supplementary bonding in the bathroom is applied to extraneous-conductive-parts and exposed-conductive-parts to reduce the potential difference between them to a level that is deemed safe in fault conditions - 50V.

To determine this, firstly, measure the resistance between all parts which may be extraneous and the Main Earthing Terminal.
If greater than 23kΩ (some prefer 46kΩ) then the part is considered not extraneous and no supplementary bonding is required.

Next, measure the resistance between all the parts which are extraneous and between these parts and the CPCs of the circuits in the bathroom.
If less than 50V/Ia then supplementary bonding is not required.
Ia being that for the highest rated OPD of the circuits in the bathroom.

If, for example, there is only a 6A lighting circuit in the bathroom then resistances between parts can be less than 50/30, that is 1.66Ω
Only above that is supplementary bonding required.
With a 40A shower circuit in the bathroom the figure is 50/200, i.e. 0.25Ω.

RCDs on ALL the circuits can with other criteria allow supplementary bonding to be omitted altogether.


So depending on your situation supplementary bonding may or may not be required.
You cannot tell by looking.

As you say yours is all copper it is likely that the pipes will be extraneous but very short runs may be of low enough impedance that no supplementary bonding is needed.



Edit - figures are for B type MCBs.
 

Reply to Can't see supplementary bonding in bathroom in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
344
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
882
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Replies
32
Views
2K
Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
29

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top