Evening all,

Some of you may remember a previous post i put up not long ago about sizing of supply cable to a caravan park.
It was the cheaper option to have the DNO ramp up the voltage and blast it down to the caravan field 400m down.

So now i have a 'sub main housing' in the caravan field with a 3phase TNC-S supply. Obviously i have to drop the earth and put a stake down at the 'sub-main housing'.

My question is do i need to put a stake down at every hook up pole or can i connect them all back to the one main stake?

Maybe a stupid question but im unsure on it so worth asking!

Many thanks in advance
 
i would earth the armour of your SWA from the sub-main to the TNC-S ( just at one end), then TT rod each hook-up.
 
Evening all,

Some of you may remember a previous post i put up not long ago about sizing of supply cable to a caravan park.
It was the cheaper option to have the DNO ramp up the voltage and blast it down to the caravan field 400m down.

So now i have a 'sub main housing' in the caravan field with a 3phase TNC-S supply. Obviously i have to drop the earth and put a stake down at the 'sub-main housing'.

My question is do i need to put a stake down at every hook up pole or can i connect them all back to the one main stake?

Maybe a stupid question but im unsure on it so worth asking!

Many thanks in advance

MO each caravan supply would have a rod
 
it would be a lot more expensive doing it that way tho surely? if i can use the one rod for all of it then i would be cheaper to do that
it would be cheaper, but should that 1 rod's connection corrode, break, be removed by a numpty, all pitches lose their earth. also you have a much longer earth path for each pitch. you can have 2 hook-ups at each point sharing a rod between 2 (or it may even be 4, not got regs. to hand)
 
Here are a couple of pages from GN7 (amd1), it was quicker to scan this than to try and explain.

This may help.
 

Attachments

  • Caravan pitch 01.pdf
    1.2 MB · Views: 95
  • Caravan pitch 02.pdf
    1 MB · Views: 57
  • Caravan pitch 03.pdf
    1.2 MB · Views: 64
Guidance note 7 seems to say you can do either.
I would go with one at each pillar, for the reasons Tel suggested, especially if it's a site where caravans are moved around regularly.
 
Why on earth (excuse the pun) would any electrician want to rely on a single earth electrode to protect a complete caravan site?? Drive a decent depth rod at each take-off pillar and connect these rods together using the armour of the SWA cable your using for your site distribution!!

Your dealing with public safety here, not trying to save the site owner a few bob. The RCDs in these pillars are by no-means a fool proof protection!! Doing these sort of installations on the cheap is not an option, they will come back and bite you, ...and hard!!

Do the job properly, and cover your own arse in the process!! lol!!
 
To follow on from E54’s post.
An earth rod at each off take gives one of the best scenarios for a good earth nest. Each rod is supporting the others giving a wide spread.
As has been said it’s safety not the site owners profit at risk.
 
Agreed, one rod at each pitch would give a far lower overall Zs, and redundency incase of losing the earthing at one or more point.

GN7 (ref post #7) suggests the preferred way is to have a single TT earthing point at the pitch DB, but notice the 100mA (or greater) RCD protecting the distribution board supplying the cables to the pitches to give discrimination against the individual 30mA RCD's at each pitch, this also negates the argument of the R2 being slightly higher on the cable runs, as this will be relatively negligble on the TT system protected by the RCD at the pitches source DB.

I suppose you could have the best of both by including the 100mA RCD (or greater) in the topology suggested by Tony and E54 (in the TNC-S system), as this would then give some backup RCD protection in the event of a single RCD failure at the pitch.

GN7 suggests you could do it either way though, and still comply, Tony and E54's method is the best and safest solution without a doubt, but it is the most expensive.

There is nothing in the regs stopping you doing it the other way.

I will get my tin hat on now lol.
 
Last edited:
Agreed, one rod at each pitch would give a far lower overall Zs, and redundancy in case of losing the earthing at one or more point.

GN7 (ref post #7) suggests the preferred way is to have a single TT earthing point at the pitch DB, but notice the 100mA (or greater) RCD protecting the distribution board supplying the cables to the pitches to give discrimination against the individual 30mA RCDs at each pitch, this also negates the argument of the R2 being slightly higher on the cable runs, as this will be relatively negligible on the TT system protected by the RCD at the pitches source DB.

I suppose you could have the best of both by including the 100mA RCD (or greater) in the topology suggested by Tony and E54 (in the TNC-S system), as this would then give some backup RCD protection in the event of a single RCD failure at the pitch.

GN7 suggests you could do it either way though, and still comply, Tony and E54's method is the best and safest solution without a doubt, but it is the most expensive.

There is nothing in the regs stopping you doing it the other way.

I will get my tin hat on now lol.

I will say it again, The Reg's relating to TT systems seriously do need amending, this is just another example that substantiates that need!! lol!!
 

Reply to Caravan hook-up point in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
904
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top