Caravan hook-up point | Page 2 | on ElectriciansForums
Discuss Caravan hook-up point in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I've done one or two of these in the past.
Strongly advise to TT every post outlet. It's the safest way of doing things and a benefit is that the multiple rods bring down the overall ZE when they're all in circiut - you won't of course see this value on the test cert because each post outlet should be tested in isolation.
Strongly advise to TT every post outlet. It's the safest way of doing things and a benefit is that the multiple rods bring down the overall ZE when they're all in circuit - you won't of course see this value on the test cert because each post outlet should be tested in isolation.
Not sure i understand your reasoning here?? If all the rods are solidly linked via the SWA cable(s) as they should be. Why would you test each post in isolation?? (eg ...using the value of the single rod, with the linking to the rest of the system disconnected) Pretty pointless linking the multiple rods, if your going to disconnect them for testing. The whole idea, is to bring the Ra level way down, to make the campsite earthing at each post as good as it can be. Done properly you'll be at, or very close to TN values with the RCD's virtually providing additional protection...
So Yes, each rod should be individually tested when installed, and also possibly during each annual out of season testing. But ''Never'' when your testing the overall installation, at post locations!!
just had a look in regs and it says you cant earth the outlets to a pme system, they have to be connected to a rod 708.553.1.14/ 708.411.4
Reply to Caravan hook-up point in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...