I have a small caravan park with 8 pitches. Each have a Rolec Electrical Hook-Up unit fitted with a Rolec 16A Single Pole and Neutral 2 Module C Curve 6kA 30mA RCBO.
I've recently fitted meters to these units which display voltage, Current and kW. I was surprised to see that some of the caravans were displaying currents over 20A and the 16A RCBO still had not tripped. I checked this myself with a 5kW load on all 8 units and not one of the 16A RCBO's tripped.
Should these RCBO's not trip if the current goes over the rated16A?
I've recently fitted meters to these units which display voltage, Current and kW. I was surprised to see that some of the caravans were displaying currents over 20A and the 16A RCBO still had not tripped. I checked this myself with a 5kW load on all 8 units and not one of the 16A RCBO's tripped.
Should these RCBO's not trip if the current goes over the rated16A?