Engineer54
Looking at that main DNO cut-out arrangement, are you sure the earthing system is PME?? I can see no N-E connection at the neutral cut-out position. I think this is a TT system, and a badly designed and installed one too!!
As Chris stated, many MFTs and RCD testers will not test when the 50 volt touch threshold has been exceeded, which means your TT system needs improving. At the very least each hook-up panel will need to be roded. And as this is, (as i suspect) a TT system, the SWA of the hook-up in-out supply cables can link those rods together...
I doubt very much if your existing Rods have corroded away, not if they were from a decent manufacturer, which should have a life of around 30 years, even in mildly corrosive soils should give at least 20 years service!! Now the cable connections to these rods is another matter, they can deteriorate especially if non-standard connection methods are used. Always best to exothermic or braise weld rod connections that are not accessable by means of earth rod inspection boxes....
As Chris stated, many MFTs and RCD testers will not test when the 50 volt touch threshold has been exceeded, which means your TT system needs improving. At the very least each hook-up panel will need to be roded. And as this is, (as i suspect) a TT system, the SWA of the hook-up in-out supply cables can link those rods together...
I doubt very much if your existing Rods have corroded away, not if they were from a decent manufacturer, which should have a life of around 30 years, even in mildly corrosive soils should give at least 20 years service!! Now the cable connections to these rods is another matter, they can deteriorate especially if non-standard connection methods are used. Always best to exothermic or braise weld rod connections that are not accessable by means of earth rod inspection boxes....