Testing a touring site for the first time - a.n.other has been doing it for years.
Incoming TNCS to glorified shed in field, outputs to hook ups earthed by SWA sheath, not connected to the big metal dis board, terminated in plastic boxes and connected to a rod so is theoretically TT'ed.
However, the readings I was getting at the hook ups seemed too good to be true, so after disconnecting everything from the rod I measured the resistance between the rod and the earth in the dis board (the TNCS earth). Result was 25 ohms.
As I said, the rod was disconnected from ever thing, so logically the resistance was through the ground.
Is this OK?
Also, elsewhere there is a poor connection in the armour between 2 hook ups, not too bad but notable. Is it worth putting another rod at this point.