Testing a touring site for the first time - a.n.other has been doing it for years.
Incoming TNCS to glorified shed in field, outputs to hook ups earthed by SWA sheath, not connected to the big metal dis board, terminated in plastic boxes and connected to a rod so is theoretically TT'ed.
However, the readings I was getting at the hook ups seemed too good to be true, so after disconnecting everything from the rod I measured the resistance between the rod and the earth in the dis board (the TNCS earth). Result was 25 ohms.
As I said, the rod was disconnected from ever thing, so logically the resistance was through the ground.

Is this OK?

Also, elsewhere there is a poor connection in the armour between 2 hook ups, not too bad but notable. Is it worth putting another rod at this point.
 
Testing a touring site for the first time - a.n.other has been doing it for years.
Incoming TNCS to glorified shed in field, outputs to hook ups earthed by SWA sheath, not connected to the big metal dis board, terminated in plastic boxes and connected to a rod so is theoretically TT'ed.
However, the readings I was getting at the hook ups seemed too good to be true, so after disconnecting everything from the rod I measured the resistance between the rod and the earth in the dis board (the TNCS earth). Result was 25 ohms.
As I said, the rod was disconnected from ever thing, so logically the resistance was through the ground.

Is this OK?

Also, elsewhere there is a poor connection in the armour between 2 hook ups, not too bad but notable. Is it worth putting another rod at this point.

I don't understnad what you're saying. Are you saying the TNCS Earth was 25 ohms?

why put a rod in for a poor connection between 2 hook up points? Don't the connections need improving/fixing?
 
I understand that it's a TT earthing system, but I dont understand the scenario described? If the earth between 2 hookups(for example the SWA isn't terminated correctly causing a 'poor connection') why stick a rod in?
 
I understand that it's a TT earthing system, but I dont understand the scenario described? If the earth between 2 hookups(for example the SWA isn't terminated correctly causing a 'poor connection') why stick a rod in?

'cos its corroded badley and I cant get anymore slack on them to make them off properly, ideally it would be easiest to leave that junction alone and sick a rod in.

On part 1 its 25 ohms between the source TT rod and the TNCS earth
 
I understand that it's a TT earthing system, but I dont understand the scenario described? If the earth between 2 hookups(for example the SWA isn't terminated correctly causing a 'poor connection') why stick a rod in?

Because you cannot use TN-CS for caravan sites so you have to convert to TT
 
Yes, and the fact that there only seems to be a resistance of 25ohms between the earth rod and the TNCS eathing

I am wondering if you might possibly have a N-E fault on the TT side somewhere, this would give you that type of reading, might be worth checking, although as everything should be RCD'd on this side anyway this might not be likely.

Remember the N is effectively joined to the TNC-S E via the CNE link at the origin.

Just a thought.
 
If the earth rod has been completely disconnected from the system and you are measuring a value of 4 ohms between the Line and SWA earth on a loop test, i'd be certainly wondering where that 4 ohms is actually coming from??

How many caravan pitches is this single earth electrode position covering?? Personally i'd have a rod position at each hook-up, you're almost guaranteed a decent working TT system then...
 
The worst Zs reading I have had so far is aroung the 5ohm area, which seems too good to be true.
System is 5 sets of 16mm SWA feeding between 6 to 8 hookup points, with each point having 4 outlets with their own RCD's and MCB's at 10 & 16.
 

Reply to Caravan hook ups in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top