I was asked to test five caravan pitches for someone I've done a few jobs for. Now, I'll admit my knowledge on TT systems is not vast so I'm looking for a bit of advice. The install has been tested by a large local contractor every three years. When I got there the setup was as follows. BS 1361 cutout - meter- 63 amp 100mA rcd - 16mm Swa - 5 way db (63amp 30mA main switch) (roughly 20m away),then out to the hookups via 10 amp mcb's. There was a 10mm earth out to multiple rods connected to the RCD steel enclosure (as told by customer). There was also a 16mm earth to the PME cutout? I know this is incorrect so I disconnected it and got 110 ohms Ra. This is obviously classed as stable but not ideal. My problem is, why did this other contractor not pick up on this, or am I the one that's wrong?? Before anyone else pipes up I know there are other faults ie no overload protection on the supply to the 5 way db!
Thanks for reading!