Any one heard of earthing cat wire,
Pict
I,v heard of earthing the tray(s) but cat wire over head for 25mm armour never, but a guy reckons it,s a must but no metion in the book only a referance to table 42a item 35
P
Nope, that's a new one on me.Any one heard of earthing cat wire,
Pict
He is a very clever chap I think I will try to find out his thinking on this, he is ex power station type so could be somthing unique to that
Pict
I,v heard of earthing the tray(s) but cat wire over head for 25mm armour never, but a guy reckons it,s a must but no metion in the book only a referance to table 42a item 35
P
I remember one of the medium sized warehouses lighting, being completely wired in a made for purpose high tensile steel wire catenary system, with proper system take-off boxes, the whole nine yards so-to-speak. No idea if such systems are still available or still used. Can't remember ever having any problems with the system during the time i was there!!
Pretty sure that the catenery system was fully earthed too.
Whilst there is an argument that a cat wire need not be bonded to earth, I think that within the Regs there are also arguments that it should be because it is an extraneous conductive part of the wiring systems, no different in essence to trunking, ladder rack, basket or conduit, and unless they were made from non-conductive materials we never balk at bonding these, so within s411 (If memory serves) it should be bonded and as part of s522 concerning the Selection and Erection of Wiring Systems (again if I have remembered the section correctly)
I would also proffer the argument that if this is between buildings and could be subject to the effects lightning (Directly or indirect by induction) then is should be bonded to earth as per BS EN 62305..
Whilst there is an argument that a cat wire need not be bonded to earth, I think that within the Regs there are also arguments that it should be because it is an extraneous conductive part of the wiring systems, no different in essence to trunking, ladder rack, basket or conduit, and unless they were made from non-conductive materials we never balk at bonding these, so within s411 (If memory serves) it should be bonded and as part of s522 concerning the Selection and Erection of Wiring Systems (again if I have remembered the section correctly)
I would also proffer the argument that if this is between buildings and could be subject to the effects lightning (Directly or indirect by induction) then is should be bonded to earth as per BS EN 62305..
Whilst there is an argument that a cat wire need not be bonded to earth, I think that within the Regs there are also arguments that it should be because it is an extraneous conductive part of the wiring systems, no different in essence to trunking, ladder rack, basket or conduit, and unless they were made from non-conductive materials we never balk at bonding these, so within s411 (If memory serves) it should be bonded and as part of s522 concerning the Selection and Erection of Wiring Systems (again if I have remembered the section correctly)
I would also proffer the argument that if this is between buildings and could be subject to the effects lightning (Directly or indirect by induction) then is should be bonded to earth as per BS EN 62305..
The systems you are describing are ''Exposed'' Conductive Parts not Extraneous. Like wise you would ''Earth a catenary wire, not bond it, as they too, would be unlikely to bring an extraneous earth potential into a building. The catenary wire would be a wholly external installation fixed to outside structures, or wholly internal installation...
I'd stongly suggest a read of part2 (definitions) of 7671. Extraneous conductive parts and conductive parts.
I would suggest you use the Index of 7671 and look under Extraneous Conductive Parts > Bonding and that is the section it points you too, just double checked in case my memory was off..as I admitted it could be in my post.
I strongly suggest that i do know the difference, and if you check my posts I did not state whether the cat wire should or should not be bonded because I do not have an opinion on the matter, I have only offered up a couple of points in the regs that could be used to justify a demand for bonding.
I strongly suggest that i do know the difference, and if you check my posts I did not state whether the cat wire should or should not be bonded because I do not have an opinion on the matter, I have only offered up a couple of points in the regs that could be used to justify a demand for bonding.
Nope, that's a new one for me.Any one heard of earthing cat wire,
Pict
I don't need to check, i know full well, that the items you suggest are ''Extraneous Conductive Parts'' are NOT!! They are part of an electrical installation that need to be ''Earthed'' not main ''Bonded''!!
You clearly dont.
That is evident from your posts.
Sorry to be persistant on this but one of the constant frustrations of this forum for me is the number of electricians who lack basic understanding of the difference between earthing and bonding,when both are appropriate or not,and the use of incorrect terminolgy which only serves to feed the confusion.
You cant have 'An extraneous conductive part of the wiring systems' ,it's not possible.
Sorry bud, but these two have pretty much nailed it on the head.
Sorry bud, but these two have pretty much nailed it on the head.
I'd take what OS says sometimes, with a pinch of salt.
I vaguely remember, from his introductory speech, he likes to be 'controversial', hence his name (his words)!!!!
Or he's making some really basic mistakes!?!?!
BS 7671:2008 said:Exposed-Conductive-Part. Conductive part of equipment which can be touched and which is not normally live, but which may become live under fault conditions.
Extraneous-Conductive-Part. A conductive part liable to introduce a potential, generally Earth potential, and not forming part of the Electrical Installation