I remember one of the medium sized warehouses lighting, being completely wired in a made for purpose high tensile steel wire catenary system, with proper system take-off boxes, the whole nine yards so-to-speak. No idea if such systems are still available or still used. Can't remember ever having any problems with the system during the time i was there!!

Pretty sure that the catenery system was fully earthed too.

Not seen them for years, we had a few set ups like you mention. they were all removed after the catenary broke at another works. They were on steel hangers in steel framed buildings so be default they were earthed.
 
Whilst there is an argument that a cat wire need not be bonded to earth, I think that within the Regs there are also arguments that it should be because it is an extraneous conductive part of the wiring systems, no different in essence to trunking, ladder rack, basket or conduit, and unless they were made from non-conductive materials we never balk at bonding these, so within s411 (If memory serves) it should be bonded and as part of s522 concerning the Selection and Erection of Wiring Systems (again if I have remembered the section correctly)

I would also proffer the argument that if this is between buildings and could be subject to the effects lightning (Directly or indirect by induction) then is should be bonded to earth as per BS EN 62305..
 
Whilst there is an argument that a cat wire need not be bonded to earth, I think that within the Regs there are also arguments that it should be because it is an extraneous conductive part of the wiring systems, no different in essence to trunking, ladder rack, basket or conduit, and unless they were made from non-conductive materials we never balk at bonding these, so within s411 (If memory serves) it should be bonded and as part of s522 concerning the Selection and Erection of Wiring Systems (again if I have remembered the section correctly)

I would also proffer the argument that if this is between buildings and could be subject to the effects lightning (Directly or indirect by induction) then is should be bonded to earth as per BS EN 62305..

I don't think there is a requirement to bond it, same as a piece of steel conduit used to carry t+e,
however I would probably and usually bond it.
 
Whilst there is an argument that a cat wire need not be bonded to earth, I think that within the Regs there are also arguments that it should be because it is an extraneous conductive part of the wiring systems, no different in essence to trunking, ladder rack, basket or conduit, and unless they were made from non-conductive materials we never balk at bonding these, so within s411 (If memory serves) it should be bonded and as part of s522 concerning the Selection and Erection of Wiring Systems (again if I have remembered the section correctly)

I would also proffer the argument that if this is between buildings and could be subject to the effects lightning (Directly or indirect by induction) then is should be bonded to earth as per BS EN 62305..

The systems you are describing are ''Exposed'' Conductive Parts not Extraneous. Like wise you would ''Earth a catenary wire, not bond it, as they too, would be unlikely to bring an extraneous earth potential into a building. The catenary wire would be a wholly external installation fixed to outside structures, or wholly internal installation...
 
Whilst there is an argument that a cat wire need not be bonded to earth, I think that within the Regs there are also arguments that it should be because it is an extraneous conductive part of the wiring systems, no different in essence to trunking, ladder rack, basket or conduit, and unless they were made from non-conductive materials we never balk at bonding these, so within s411 (If memory serves) it should be bonded and as part of s522 concerning the Selection and Erection of Wiring Systems (again if I have remembered the section correctly)

I would also proffer the argument that if this is between buildings and could be subject to the effects lightning (Directly or indirect by induction) then is should be bonded to earth as per BS EN 62305..

I'd stongly suggest a read of part2 (definitions) of 7671. Extraneous conductive parts and conductive parts.
 
The systems you are describing are ''Exposed'' Conductive Parts not Extraneous. Like wise you would ''Earth a catenary wire, not bond it, as they too, would be unlikely to bring an extraneous earth potential into a building. The catenary wire would be a wholly external installation fixed to outside structures, or wholly internal installation...

I would suggest you use the Index of 7671 and look under Extraneous Conductive Parts > Bonding and that is the section it points you too, just double checked in case my memory was off..as I admitted it could be in my post.

I'd stongly suggest a read of part2 (definitions) of 7671. Extraneous conductive parts and conductive parts.

I strongly suggest that i do know the difference, and if you check my posts I did not state whether the cat wire should or should not be bonded because I do not have an opinion on the matter, I have only offered up a couple of points in the regs that could be used to justify a demand for bonding.
 
if it were extraneous it would require main bonding of the appropriate size. I could see this being the case if it was attached to a metal pole in the ground. however the wire itself and any brackets wouldn't meet the definition of an extraneous conductive part or an exposed conductive part, even if used to carry t+e and just attached to masonary etc. between two buildings.
 
Last edited:
If someone can please explain to me how a catenary wire is ever going to bring an extraneous earth into a building?? Or come to that, why you would ''bond'' rather than earth, a catenary wire??
 
I would suggest you use the Index of 7671 and look under Extraneous Conductive Parts > Bonding and that is the section it points you too, just double checked in case my memory was off..as I admitted it could be in my post.



I strongly suggest that i do know the difference, and if you check my posts I did not state whether the cat wire should or should not be bonded because I do not have an opinion on the matter, I have only offered up a couple of points in the regs that could be used to justify a demand for bonding.


I don't need to check, i know full well, that the items you suggest are ''Extraneous Conductive Parts'' are NOT!! They are part of an electrical installation that need to be ''Earthed'' not main ''Bonded''!!


Likewise Wirepuller didn't say anything about cat wires, he just rightly pointed you to the definitions of extraneous conductive parts and conductive parts in BS7671.
 
Last edited by a moderator:
I strongly suggest that i do know the difference, and if you check my posts I did not state whether the cat wire should or should not be bonded because I do not have an opinion on the matter, I have only offered up a couple of points in the regs that could be used to justify a demand for bonding.


You clearly dont.
That is evident from your posts.
Sorry to be persistant on this but one of the constant frustrations of this forum for me is the number of electricians who lack basic understanding of the difference between earthing and bonding,when both are appropriate or not,and the use of incorrect terminolgy which only serves to feed the confusion.
You cant have 'An extraneous conductive part of the wiring systems' ,it's not possible.
 
Last edited by a moderator:
I don't need to check, i know full well, that the items you suggest are ''Extraneous Conductive Parts'' are NOT!! They are part of an electrical installation that need to be ''Earthed'' not main ''Bonded''!!

You clearly dont.
That is evident from your posts.
Sorry to be persistant on this but one of the constant frustrations of this forum for me is the number of electricians who lack basic understanding of the difference between earthing and bonding,when both are appropriate or not,and the use of incorrect terminolgy which only serves to feed the confusion.
You cant have 'An extraneous conductive part of the wiring systems' ,it's not possible.

Sorry bud, but these two have pretty much nailed it on the head.
 
Ah, good question! I think as this particular nail is reinforced plastic, then neither! Now stop advocating the earthing/bonding of plastic Tel! You'll confuse the 5WWs :D
 
Sorry bud, but these two have pretty much nailed it on the head.

I have to disagree, but as I only stated that there is an argument for both sides of the coin, and really don't care either way as I have never and never would earth centenary wire unless there was an exceptional reason to, for me it is a moot point and I refer the previous two back to the definitions in the regs because they classify centenary as an EXTRANEOUS and not an EXPOSED conductive part...but hey ho.
 

Reply to Catenary wire in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

While there are some valid points, no-one has mentioned the most important. YOU NEED THE RIGHT PLUGS. "RJ45"* plugs come in different types...
Replies
9
Views
923
Brilliant. Thanks Brian much appreciate the advice.
Replies
2
Views
234

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top