Excellent answer and true we hope RCDs will operate at 30 or 40 mA but.....the earth in T&E has always been a smaller dia than the current carrying cables longgggg before RCDs ELCBs were considered a necessity and there is still the question of an un sheathed cale. So what you are saying is if you buy a piece of general purpose three core to wire up a a piece of electrical equipment the earthy core is already sheathed in the outer sheath and there fore a seperate sheath is not necessary. But it is sheathed!:wink_smile:The cpc is not insulated, but it is sheathed in T&E. That is considered adequate when part of a cable.
The cpc is allowed to be smaller in fixed installation cables such as T&E because using the adiabatic equation, it is assumed that the duration of the earth fault current is so short that none of the heat energy produced in the protective conductor escapes before the protective device operates. Although not entirely accurate, it is close enough to satisfy BS7671.
Hope that helps
Surely its not that difficult to put a sheath around it? It would take away the necessity to sheath it at either end when making off. Well as an old stager thats my believe.
Having 'leccy'd' in France a lot of what the French leccy's do is far and away better to the way Brits do it and having a sheathed earth of the same diameter as the current carrying cables is one of 'em.
Sorry being pedantic again I'll get me coat!
Fred