brucelee
-
Hi All
I have a question regarding correct certification
I carried out some work which included a CCU change , New shed supply and final circuits , another new circuit and some replacement acessories so issued a EIC for additions and alterations to an existing
I have then had to go back and carry out urgent remedial work as there was L-N IR fault on the house lighting
couldnt rectify fault at time of above has had to seek permission from customer regarding removal of wood flooring and carpets so I isolated the circuit and locked off as well as informing the customer I had already rectified mutlipe loose connections and hidden connector blocks in loft under a ton of insualtion Not taped nothing the Resistance was apporaching 6 ohms
I then got permission to carry out the work as well as some additional work
So I traced the fault it was a Pendent base shoved under flooring above original half of kitchen the Neutral flex was jsut hanging by about 3 stranded Visible heat damage to it and the neutral terminal and the loops had nearly burned through to the neutrals on the 3 plate pendent base No lid even then connector blocks 2.5mm T/E looped in and out and more connector blocks with 1.0mm T/E to Gu10s installed at side of beams etc
It was done when He had his kitchen extended and a new fitted kitchen this is only one of many issues and faults I have found
So rewired, repositioned, removed from house lighting and added to existing kitchen circuit which is a kitchen extension
so as to create 1 circuit for all the kitchen and utility and remove some of the load from existing hosue lights
I also installed a new supply for existing outside lighting from a RCBO and installed 2 new FCUs 1 for existing soffit lights and 1 for existing security light
I have then replaced a wall fan like for like in bathroom but altered the wiring as it was previously fed from a shower circuit at the 30dp pull switch which has now been removed
so I have teken new feed from existing house lighting and installed a 3A FCU and then a 3 pole Isolator pull switch the load leg is the existing as couldnt change due to damge to decoration Ie tiles
Would you issue a EIC for the LOT
OR
Would you issue a EIC for the NEW supply to the existing outside lights
and 2 MEIWCs for the additions and alterations to the other circuits
I would Like your opinions on the certification you would issue as ELECSA and MY relevent books differ in whats certification is required
I thought EIC and so does some of my books but elecsa think otherwise
Thanks
I have a question regarding correct certification
I carried out some work which included a CCU change , New shed supply and final circuits , another new circuit and some replacement acessories so issued a EIC for additions and alterations to an existing
I have then had to go back and carry out urgent remedial work as there was L-N IR fault on the house lighting
couldnt rectify fault at time of above has had to seek permission from customer regarding removal of wood flooring and carpets so I isolated the circuit and locked off as well as informing the customer I had already rectified mutlipe loose connections and hidden connector blocks in loft under a ton of insualtion Not taped nothing the Resistance was apporaching 6 ohms
I then got permission to carry out the work as well as some additional work
So I traced the fault it was a Pendent base shoved under flooring above original half of kitchen the Neutral flex was jsut hanging by about 3 stranded Visible heat damage to it and the neutral terminal and the loops had nearly burned through to the neutrals on the 3 plate pendent base No lid even then connector blocks 2.5mm T/E looped in and out and more connector blocks with 1.0mm T/E to Gu10s installed at side of beams etc
It was done when He had his kitchen extended and a new fitted kitchen this is only one of many issues and faults I have found
So rewired, repositioned, removed from house lighting and added to existing kitchen circuit which is a kitchen extension
so as to create 1 circuit for all the kitchen and utility and remove some of the load from existing hosue lights
I also installed a new supply for existing outside lighting from a RCBO and installed 2 new FCUs 1 for existing soffit lights and 1 for existing security light
I have then replaced a wall fan like for like in bathroom but altered the wiring as it was previously fed from a shower circuit at the 30dp pull switch which has now been removed
so I have teken new feed from existing house lighting and installed a 3A FCU and then a 3 pole Isolator pull switch the load leg is the existing as couldnt change due to damge to decoration Ie tiles
Would you issue a EIC for the LOT
OR
Would you issue a EIC for the NEW supply to the existing outside lights
and 2 MEIWCs for the additions and alterations to the other circuits
I would Like your opinions on the certification you would issue as ELECSA and MY relevent books differ in whats certification is required
I thought EIC and so does some of my books but elecsa think otherwise
Thanks