hi chris
they said the heating was coming on during the night and it was very warm.
like i described I set the times on the programmer to see if they come on and off as they should and it does. Do you think as its getting warm when its ment to be off that it could be a faulty programmer? they say when it comes on in the night the programmer shows it being off any thoughts.
thanks
"Hello mcm",
I have never come across a Programmer that caused this to happen - in the last 40 Years that I have been a Heating Installer / Engineer.
Especially as You mentioned that when the Boiler / Heating is On the Programmer shows that it is Off - But I would be interested to see if any of the Electrical Professionals on here do know whether this could ever happen regarding an `Internal Malfunction` of the Programmer - ?
When this happens do You happen to know whether the People in the Home decide to Turn Off the Boiler ? - How have they said that the Heating goes Off - Or does it then continue when the Programmer Setting comes to the Morning `On` Time ?
THIS is very unlikely But:
I am wondering if the Boiler Frost Protection Thermostat is Turning On the Boiler and instead of allowing it to just Fire for a short period of time to `Warm` the Boiler [and as a result of that the surrounding Pipework] - it is not Turning Off the Boiler after a small rise in the Temperature but is allowing it to run for a much longer period of time - ?
That would be a Very Strange situation because at what point would the Frost Protection Thermostat then `Turn Off` the Boiler ?
IF the situation with the Heating Turning On is caused by the Boiler Frost Protection Thermostat and the Boiler is then continuing to Run into the Morning `On` Period as determined by the Programmer because the Frost Thermostat is NOT Turning the Boiler Off when it should perhaps then the Frost Thermostat is being `Overridden` by the Operation of the Programmer / Switched `On` and then the Boiler / Heating System works correctly until the operation of the Frost Protection Thermostat again - ??
I would strongly advise that You contact the Boiler Manufacturer Technical Helpline to ask whether this CAN Happen as they would obviously know more about the `Internal Components and Electrical System` than We could ever `Diagnose` on here.
All of the Well Known Boiler Manufacturers have good Technical Helplines - although obviously they are run to be used by mainly Heating Installers / Engineers. - I would suggest that they will probably advise You that this should be looked at by a Boiler Servicing Engineer - You should obviously not speak as if You would be doing any work to the Boiler.
If that is the case You should definitely advise the People in the Home to arrange for an Engineer who actually works for the Boiler Manufacturer to Inspect / Test the Boiler - NOT an Independent Boiler Engineer - If only because the Manufacturers Engineer would have the Facility to Change the Frost Protection Thermostat straight away if He suspects that is causing the Problem - NOT `Have to Order the Stat`.
Obviously whether the Boiler is being Turned On by the Frost Protection Thermostat or the Programmer the Boiler [Heat] Thermostat governs the `Firing` of the Burners [Room Thermostat should not operate with Frost Protection] - SO even IF the fault is the Frost Thermostat causing the Boiler to be Turned On during the Night - the Boiler Thermostat [Heat Setting] will cause the Burners to be Turned On / Off.
I mention this in case anyone reading the Posts wonders why the Boiler does not just `Keep Firing` if turned on by the [Faulty ?] Frost Protection Thermostat.
I cannot think of any other cause of what You described - I hope to see a couple of opinions about the possibility of the Programmer Malfunctioning and causing this - ?
"Sorry" - that I cannot give You a Definitive Answer to this - In My experience it is a Unique Situation ! - as I have not encountered this - although a Boiler Service Engineer MAY have ?
Regards,
Chris