Just wondered what you all think about one of the changes to the regs.
Having to install an earth rod when changing a consumer unit.
 
Hi J, IIUC with an upfront RCD (same position as TT case) the RCD would sense current in L and not N as it's now going back through the rod. And so it'd trip. We would still need a rod (at the PME terminals in your pic) but now we just use it to disconnect the installation rather than put in many rods and try to keep touch voltages down.
 
Last edited:
But it's not fault current, it's any residual installation neutral return current which is able to lift the MET and all exposed conductive parts. The neutral current is surely still balanced in the tails since it's got to be the same as any live current. (There is no earth fault in the installation during this condition to make it otherwise)
 
I can see the logic in it to be honest IET have produced guidance notes on this before but NICEIC inspectors would give you a berating for having 2 different earthing arrangements . So when you are asked for earthing arrangement at origin what would you put down TNCS, TT or will there be a new classification code TNCS/TT?
Would you have to install a rcd on tails from the meter before they enter an AMD 3 board rated at 30mA, or would you be able to install an rcd with upto 1A tripping current as it is for a dribution circuit on a TT system? Could you decide to ignore the TT side of it and continue as for TNCS as the TT part would only come into play when DNO lose neutral on their network. I don’t mind as I am on a trusty old TNS supply at the moment lol.
 

Reply to Changes are coming, what do you all think in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
301
  • Article
The mcb used will be sized for the spd cable.
Replies
4
Views
428

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top