hi guys an gals
what's phase sequencing about?
big al

presumably you mean the requirement to verify that the phase sequence is maintained?

dont know what level you are at (so i will assume you dont know)

in a three phase sytem, each phase is angularly 120 degrees apart. the order that these phases 'peak' in (their waveforms) is the phase sequence

in old money, this was conventionally Red-Yellow-Blue, or L1, L2 L3.

The requirement is to verify that if it starts in that order it should finish in that order, with the main problem of motors running in reverse DOR if it doesnt.
 
Thanks for getting back guys
Context is 2 fold: 1) PIR certificate askes for 'verification of phase sequence' What's the test process for this?. 2) reg 612.12: 'For multiphase circuits, it shall be verified that the phase sequence is maintained'? Is this a good enough explanation?
Cheers in anticipation of your replies.
big al
 
Thanks for getting back guys
Context is 2 fold: 1) PIR certificate askes for 'verification of phase sequence' What's the test process for this?. 2) reg 612.12: 'For multiphase circuits, it shall be verified that the phase sequence is maintained'? Is this a good enough explanation?
Cheers in anticipation of your replies.
big al

common mis-conception Big Al, it says VERIFY, not test.

If i look at one end of a run of SWA,(for example)
and the conductors are labelled, and connected to L1, L2 and L3, and i look at the other end, and they are the same, then i have verified that the phase sequence is maintained. Of course you could do a live test (f you have phase sequence or phase rotation on your meter), you could also dead test (by doing R1+R2 checks on each relevanet phase) or just look as i have said:)
 
What do you have to do with your 16th edition testers??
I need to purchase one and the little man in the shop said that he had no 16th edition ones in stock and he was waiting for the 17thedition ones to come in.

---------
Brook

Sreevysh Corp
 
Re junction boxes, their is a regulation somwhere that says a tool is required to remove the lid. This outlaws the old jb`s with the lids that screw on whith out screws.
 
I know of no regulation that says a JB requires a tool to open it:confused:

The new JB from Hager just snap close
 
Last edited by a moderator:
The 17th Ed requires you to verify the phase rotation (or sequence) on the part of the system upon which you are working. Newer testers have this facility BUT voltage testers are already available that have this facility built in (albeit a cut down version) for about £30-£40 so don`t ditch your 16th Ed test equipment, there`s nothing wrong with it, just buy a small tester for the odd occasion you need to work on three phase.


If anyone`s interested I can sell them a single phase rotation tester for £200.;)
 

Reply to the thread, titled "Changes in the 17th edition...." which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top