I had a bit of a nightmare on saturday. Job was to change a CU.
Problems found
1. No earths on both lighting circuits. There was an earth present but DIY Dave has been in an didnt connect many of the earths up, left some hanging loose. So I told the guy that we need to remove all metal fittings and replace with plastic. There was also a N-E fault somewhere on both lighting circuits. He is fine with me coming back to sort out the lights, there are about 40 ELV downlights too as he wants his metal fittings and switches back.
2. The immersion is on the same circuit as the upstairs radial. Now i know that this should be on its own circuit but i cant see it as dangerous, it could just end up in annoying tripping of the MCB. Does this immersion need to be put on its own circuit or can it be left and just mentioned on the cert
3. The boiler is plugged into a socket that is on the lighting circuit. Again, this is not the done thing, but i dont see it as dangerous. The worst that could happen is that something could be plugged in that will cause the breaker to trip. Again, does this need sorting or can i just label the socket 'boiler only' and mention on the cert
4. One of the sockets radials had a dead short between L and N. We physically searched everywhere we could to find a load with no joy. Does this further investigation or can i just put n/v (not verified) on the cert. Everything works fine
5. The hot tub was so close to the isolator that i couldnt get it off to test. Was going to put it as something i couldnt test but as i am going back, he is going to empty it so i can test the cable for R1+R2.
I also found the kitchen circuit had a LN insulation resistance of 1.09M. He says he is going to have a new kitchen and he will get the kitchen fitters to sort that when they fit the kitchen (i dont believe this, i reckon he and his dad are going to fix or rewire the kitchen)
The guy has recently moved into the house as i think is planning on doing a lot of DIY electrics (like rewiring his garage) so i really need to cover myself.
He wants a certificate for the job but doesnt want to pay for anything that doesnt strictly need doing except for the lights as his wife like the metal lights and switches.
To recap.
Does the immersion need to put on its own circuit
Does the boiler socket on the lights need sorting
Does the radial with the load/short need finding or can i put N/V on the cert with an explanation
Problems found
1. No earths on both lighting circuits. There was an earth present but DIY Dave has been in an didnt connect many of the earths up, left some hanging loose. So I told the guy that we need to remove all metal fittings and replace with plastic. There was also a N-E fault somewhere on both lighting circuits. He is fine with me coming back to sort out the lights, there are about 40 ELV downlights too as he wants his metal fittings and switches back.
2. The immersion is on the same circuit as the upstairs radial. Now i know that this should be on its own circuit but i cant see it as dangerous, it could just end up in annoying tripping of the MCB. Does this immersion need to be put on its own circuit or can it be left and just mentioned on the cert
3. The boiler is plugged into a socket that is on the lighting circuit. Again, this is not the done thing, but i dont see it as dangerous. The worst that could happen is that something could be plugged in that will cause the breaker to trip. Again, does this need sorting or can i just label the socket 'boiler only' and mention on the cert
4. One of the sockets radials had a dead short between L and N. We physically searched everywhere we could to find a load with no joy. Does this further investigation or can i just put n/v (not verified) on the cert. Everything works fine
5. The hot tub was so close to the isolator that i couldnt get it off to test. Was going to put it as something i couldnt test but as i am going back, he is going to empty it so i can test the cable for R1+R2.
I also found the kitchen circuit had a LN insulation resistance of 1.09M. He says he is going to have a new kitchen and he will get the kitchen fitters to sort that when they fit the kitchen (i dont believe this, i reckon he and his dad are going to fix or rewire the kitchen)
The guy has recently moved into the house as i think is planning on doing a lot of DIY electrics (like rewiring his garage) so i really need to cover myself.
He wants a certificate for the job but doesnt want to pay for anything that doesnt strictly need doing except for the lights as his wife like the metal lights and switches.
To recap.
Does the immersion need to put on its own circuit
Does the boiler socket on the lights need sorting
Does the radial with the load/short need finding or can i put N/V on the cert with an explanation