A couple of points.
You say the CU is in a metal cupboard, is this a skeleton board, where the metal cupboard is the outer case of the CU?
If it is, then I suggest doing a search for skeleton board, and you should be able to find some info.
Yes you can have a CU wth a single 30mA RCD, but you would not be able to have it cover all of the circuits.
Someone mentioned something about the cables being in 'steel' conduit, not certain in what context, but there's no requirement in BS7671 for anything other than earthed metallic conduit?
In many instances the conduit was used as the CPC, and now due to corrosion the conduit is not good enough to still be used as the CPC.
You may find it very hard to pull out the existing cables and even harder to pull in T&E. It may well be easier to use singles.
 
Just to update:
The NICEIC have confirmed that DCS electrical.com are not not on the NICEIC roll and are being added to their wall of shame
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
chnaging CU
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
96

Thread Tags

Advert

Thread statistics

Created
electrician4u,
Last reply from
Geordie Spark,
Replies
96
Views
8,054

Advert

Back
Top