No problem with a connector block as long as you have the room available, its probably less likely to fail than a through crimp.
 
my gaffer told me we got pulled on having chock block in the back of a switch box by the NIC inspection and that it must be a sealed connection i.e wago or crimp etc. :confused:
 
Got called to a job yesterday to check 8 double sockets in a bedroom that had been installed by a bloke he knows a couple of months ago. As the room is going to be used for work and is going to have a couple of people working in there he wanted to make sure its safe.

To cut a long story short the fella has extended the ring to these 8 sockets however he has used choc boxes in two of the sockets to extend the cable.

Question is, is this aloud ? if not what would be the solution to extend the cable, when the floors are solid wood ! does not look pretty would be best to crimp ?

Any ideas ??:rolleyes:

How do you get one of these.......

[ElectriciansForums.net] Choc boxes in the back of sockets


........in the back of a socket. :D
 

Reply to Choc boxes in the back of sockets in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
564
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
937

Similar threads

How many and what type of cables do you want to join, Chocbox is the last thing I would use.
Replies
3
Views
695
A problem putting multiple cores into a ferrule is when you need to do testing or fault finding. You can't just drop the ends out of the terminal...
Replies
2
Views
284

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top