Finally I found it!
Russian Standard 50571.5-94 links to P-IEC 60364-4-43 ed1.0 (withdrawn, publication date 1977-01-01).
My mistake. Sorry. I read reg. 433.1 not well. I missed note 2.
So. Cables are not derated 50%.
IMHO. Note2 applies to light circuit and outlet circuit. I2<=Iz is better requirement for overload protection in that case.
Russian Standard 50571.5-94 links to P-IEC 60364-4-43 ed1.0 (withdrawn, publication date 1977-01-01).
Russian Standard 50571.5-94
Overload protection
1) Ib <= In <= Iz
2) I2 <= 1.45Iz
Note
Protection in accordance with this paragraph does not provide complete protection in some cases, such as long-term overcurrent smaller in value than I2, and do not always cost-effective solution.
It is assumed that the electric network is designed so that the small
overload with long duration will not occur often.
My mistake. Sorry. I read reg. 433.1 not well. I missed note 2.
BS7671
433.1
Every circuit shall be designed so that a small overload of long duration is unlikely to occur.
433.1.1
...........
NOTE2
Protection in accordance with this regulation may not ensure protection in all cases, for example, where sustained overcurrents less than I2 occur.
So. Cables are not derated 50%.
IMHO. Note2 applies to light circuit and outlet circuit. I2<=Iz is better requirement for overload protection in that case.