Circuit breaker testing | Page 2 | on ElectriciansForums

Discuss Circuit breaker testing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Yeah, maybe 'days' was overstating it somewhat but even at 1.5 x the rated current which would be a sensible lower point you'd probably be in for an hour or so test time depending on the curve.


According to this document kindly pinned by Lenny on this thread the UK regs state that where two or more faults have occurred between the Ics and Icu values of the MCB the continued operation of the circuit breaker must be verified? Do they outline the verification procedure anywhere?

Not aware of any set verification procedures, but it's generally taken that testing MCB'S, MCCB's, ACB'S and the like, measuring at least 2 points on it's thermal protection curve, will verify that, that side of unit is in good condition for service, then of course a test(s) on the magnetic side of things. Obviously where adjustable parameters are present more tests would be prudent. But then with such breakers, internal/external current coils would likely be the case and then the tests, will generally be conducted through the coils with secondary injection test equipment...

Most larger frame size MCCB / ACB / etc Breakers, will generally have test provision for a manufacturers own protection proving unit!!
 
If MCB testing was mandatory, where would we stop? Test the DNO fuse to make sure it's going to blow?

Fuses can't be tested, but are still considered safe as the manufacturing processes are so tight.

Personally never heard of an "incident" caused by an MCB failing to trip (although I am new to the game)

The OPs point about second hand is perfectly reasonable though, you'd never know with a pre-owned MCB... It could be brand new and just have been taken out the packaging by mistake, or it could have been dropped in a bucket of water...
 
Last edited:
If MCB testing was mandatory, where would we stop? Test the DNO fuse to make sure it's going to blow?

Fuses can't be tested, but are still considered safe as the manufacturing processes are so tight.

Personally never heard of an "incident" caused by an MCB failing to trip (although I am new to the game)

The OPs point about second hand is perfectly reasonable though, you'd never know with a pre-owned MCB... It could be brand new and just have been taken out the packaging by mistake, or it could have been dropped in a bucket of water...

Don't worry, it's never going to be mandatory to performance test MCB's for domestic installations!! lol!!!
 

Reply to Circuit breaker testing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
  • Locked
Thread closed.
2
Replies
19
Views
871

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top