Hi Peeps
I have my 2391 coming up in October and I am busy revising.
When determing the circuit length and VD, my notes say to link L - N at the load side and take the loop resistance at the DB.
The example I have is : Loop Resistance = 0.7 ohms (R) and csa of cable = 1mm2 (S), calculate the circuit length??
The formula they give is Circuit Length = 29.4 * R * S.
My question is where does the 29.4 come from??
Cheers
Mark
I always calculated circuit length by the R1 + R2 using the resistance of the cable given in the OSG guide Table 1A
So, if you divide the result of the R1+R2 test by this value it will give you the length of the cable. So say you have 2.5mm T+E with a 1.5mm CPC then that is 19.51.
You take your R1 + R2 reading and get say 0.54
0.54 ÷ (19.51 ÷ 1000) = 28.42 meters.
Is that 29.4 just a token resistivity example
Hi mate
The example they give is Circuit Length = 29.4 * R * S
The answer they give is Circuit Length = 29.4 * 0.7 * 1 = 20.6 metres
In other words they're muliplying the Loop Resistance of 0.7 by the csa of the cable 1mm2 by 29.4!!
I have never come accross this equation before? Confused.com
I think the 29.4 is made up. It's supposed to be the resistance in millohms per meter of the cable.
According to Table A.1 in GN3, it should be 36.2 when measured with an ambient temperature of 20ºC.
I think that's just a, poor, example.
Formula should be VD = ((mV/A/m) x L x Ib)/1000)
Where L is in meters and Ib is in Amps with the coefficients taken from appendix 4 of BS7671.
Aren't those values in Appendix 4, for when the conductors are at operating temperature?
I like to use the values in Table A.1 in GN3, as you don't have to apply correction factors.
Ah yes, I see what you mean, yes, just grabbed my BGB and the tables are listed as for operating temperature, oops :(
Hi Peeps
Cheers
Mark
If you've measured the l/n resistance, why do you need to work out the circuit length?
V=IR so you have R you just need the design current.
So with a L/N loop of .7 as per your example, if the design current was say 6 amps the volt drop would be .7X6 =4.2 volts. Job done.
That would actually be 0.7 x 6 x 1.2 = 5V as the resistance was measured at 20°C and volt drop needs to be corrected for the cable operating temperature of 70°C.
You're right Jud, I'm just making the point that if the cable is already installed you are just verifying the volt drop, you only need to calculate the vd when you are designing a circuit.
Or is this something required for the 2391 exam? I must admit I never came across it.
Maybe just to show that you know how to work out the length of a circuit from resistance.
I must admit I've never done it using the formula in the OP. I do it the same way as malcolm said in post #2.
So it would be...
L = R ÷ (mΩ/m ÷ 1000)
L = 0.7 ÷ (36.2 ÷ 1000)
L = 0.7 ÷ 0.0362
L = 19.33m
L = length of circuit, R = measured resistance, mΩ/m = resistance per meter of 2 x 1mm² copper conductors (from Table 9A OSG or Table A.1 GN3)
Swindon, Wilts
Circuit Length
Mark.W,
Mark.W,