The value given is a correction factor based on the resistivity of copper the csa and the fact that you are measuring twice the length.
R is resistance in ohms, rho is resistivity of copper in ohm.m, L = length in m, A = csa in m[SUP]2 [/SUP],S = csa in mm[SUP]2[/SUP]
You have R in ohms, S in mm2
To Convert A to S multiply by 1,000,000 (or S to A divide by 1,000,000)
rho= 1.7*10[SUP]-8[/SUP]=0.000000017 ohm.m
Calculation is R = rho*L /A
Therefore L = R*A /rho
L= R * S / 1,000,000*rho
L= R *S * (1/(1,000,000*rho))
Therefore L= R * S * (1/1,000,000 * 0.000000017)
L= R * S * (1/0.017)
L= R * S * 58.8
Because you are measuring twice the length of the circuit the value becomes half of 58.8 =29.4
Hope this answers the question, I think the values I used before, (from the OSG) are modified for various factors to simplify calculations.