Hi guys, after flat bashing for years, I'm now on my own and seem to only be working on TT installations. Can someone just clear this up for me please?When installing a new cu in a TT installation, do I need a 100mA time delayed main switch or can I just put a normal main switch in and have a split 30mA board.Steve
 
agree with Tel and white armour , all circuits need to be protected by an RCD on a TT circuit so a dual RCD board will cover it , possible additional RCD for the supply cables if installed in an area where they may be at risk but this RCD should be time delayed to eliminate .............brains gone what the hecks the word totally gone sorry will post when it gets to me
 
as far as i know its 21 ohms max ze for tt systems. My own house was using the water pipe for main earthing when i bought it so i just rang yedl and they put a new service in for me with t n c s link. much better.
Regards discrimination.....i work for an electrician as an apprentice and we come across bs3036 rewirables a lot which have poor dicrimination but customers dont care about that its a case of if it works its right but i would always recommend changing them for rcd board (which is a requirement for tt on the 17th ). i think time delaiyed 100ma rcds were on the 16th.
21Ω is the maximum resistance for earth rods at the supply.
The requirements for RCD protection for TT systems is the same in the 17th, as it was in the 16th.
The changes for RCD protection between the 16th and the 17th, are for socket-outlets, special locations and cables concealed in walls. Those changes are applicable whatever system is in use, TT, TN-S or TN-C-S.
 
Hi Mate
for TT its RA which is the sum of resistances of the earth electrode and the protective conductors connecting it to the exposed conductive part
RA = 50v divided by 0.03 (30mA) = 1667 ohms max rounded up but for TT anything over 200Ohms may be unstable
you can use ZS value instead as this will give you a worse case scenario if its a acceptable value with zs value then it will be with RA as this is just the protective conductor and ZS is the line and protective conductor
 
With 30mA protection, the maximum Ra is indeed 1667 Ohms but to ensure stability, BS7671:2008 and Guidance Note 8 suggest a measured maximum of 200 Ohms.Personally, I'd rather see a deep electrode with an Ra of 400 Ohms than a shallow electrode with an Ra of 100 Ohms, depth is king here to combat soil drying/freezing.Of course the lower the Ra the better, there is no minimum here!When using the '17th edition board' and hence no 100mA 'S' type RCD it should be noted that the consumer unit should be of an insulated type.
 
The 21 Ohms is the contracted maximum resistance guaranteed by the DNO at the supply just as Spinlondon said. Your max reading should be 200 but as Telectrix says, get it as low as possible and that does not include poring a bucket of water on it 5 mins before you test it infront of your asesser ;);) (i won't name any names, you know who you are) :)
 
Last edited:

Reply to clarification of cu upgrade on TT installation in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
956
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top