Class 2 light fitting | on ElectriciansForums

Discuss Class 2 light fitting in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 5, 2023
Messages
83
Reaction score
63
Location
Oxford
Hi all,

Just been to fit some lights for a customer in a couple of bathrooms. Customer supplied the fittings.
Turned up unboxed etc. fitting states it is class 2 on the packaging, as well as in the instruction manual repeatedly. Including prohibiting fitting an earth.
Attached are photos of said fitting. Single insulated cables grommeted out the metallic back (with incredibly limited scope to make the connections, or accommodate the cable from the ceiling). Fitting is entirely metal other than the "lens", with metal studs, a metallic ring that affixes to said studs retaining the lens. I'm not losing the plot, this is categorically not a class 2 double insulated fitting, right?!

Discussed with the customer and agreed I would supply suitable fittings and return to fit when I also complete their outside lights.

[ElectriciansForums.net] Class 2 light fitting


[ElectriciansForums.net] Class 2 light fitting


[ElectriciansForums.net] Class 2 light fitting
 
It is class II by design…. Now in practice sense, that means tiny little connection box… but by design, it is class II

The small box will have some for of strain relief, and in the event of a cable becoming loose… it’s only going to touch plastic. Hence “double insulated”

The brown and blue wires going to the fitting look like reinforced insulation… much tougher than regular PVC insulation… so no dangers there.

I can’t see the connections into the lampholder… but again, I suspect there’s cable grip of some sort, and it’s of plastic construction.

It’s only the metal plate of the fitting that introduces any danger… and that is solved by specifically telling you not to connect to the cpc of the supply….. where an unknown fault may have introduced a voltage potential to that cpc.
They don’t want their fitting to be at that potential where a possibly wet human being in a bathroom may be able to touch it.


The designers of the fitting cannot guarantee that rcd protection is in place, or if there’s even a cpc present…. So they design their products to class II to cover any eventuality.

Looking at end of life of products… metal can be recycled, plastic can’t….. so they’re also designing recyclability into the product.


In summery… the design is class II, but in practicality of actually working on it… PITA.
 
It is class II by design…. Now in practice sense, that means tiny little connection box… but by design, it is class II

The small box will have some for of strain relief, and in the event of a cable becoming loose… it’s only going to touch plastic. Hence “double insulated”

The brown and blue wires going to the fitting look like reinforced insulation… much tougher than regular PVC insulation… so no dangers there.

I can’t see the connections into the lampholder… but again, I suspect there’s cable grip of some sort, and it’s of plastic construction.

It’s only the metal plate of the fitting that introduces any danger… and that is solved by specifically telling you not to connect to the cpc of the supply….. where an unknown fault may have introduced a voltage potential to that cpc.
They don’t want their fitting to be at that potential where a possibly wet human being in a bathroom may be able to touch it.


The designers of the fitting cannot guarantee that rcd protection is in place, or if there’s even a cpc present…. So they design their products to class II to cover any eventuality.

Looking at end of life of products… metal can be recycled, plastic can’t….. so they’re also designing recyclability into the product.


In summery… the design is class II, but in practicality of actually working on it… PITA

Many thanks, it was just the singles dangling about that had me questioning it, but of course I was overlooking reinforced insulation being acceptable.
All for recyclable products, and appreciate why a manufacturer wants class 2 ratings, was just slightly confused as to how this was achieving that.
Junk, refuse to fit them.
Have agreed to supply a more spark friendly fixed LED unit. Client was very understanding.
 
It’s only the metal plate of the fitting that introduces any danger… and that is solved by specifically telling you not to connect to the cpc of the supply….. where an unknown fault may have introduced a voltage potential to that cpc.
They don’t want their fitting to be at that potential where a possibly wet human being in a bathroom may be able to touch it.

There are many Class I IP65 GU10 downlights out there across the UK, which all must be earthed regardless where they're fitted. Since the aforementioned ceiling fixture appears to be in a similar situation, do we really have to worry about grounding faults at all? (Please point out if I'm wrong though)
 
Playing devil's advocate.

Class 2 shouldn't really be fitted in a dwelling, class 1 would be better.
 
Last edited:
Class 2 shouldn't really be fitted in a dwelling,
I don't think there's any problem using class 2's in dwellings. I gather we can't use double/reinforced insulation as the sole protective measure for a circuit in dwellings, however, 411.1 permits class 2's when using ADS as the protective measure.
 
I don't think there's any problem using class 2's in dwellings. I gather we can't use double/reinforced insulation as the sole protective measure for a circuit in dwellings, however, 411.1 permits class 2's when using ADS as the protective measure.
Can ADS be provided in the absence of a cpc. ?

Also:
412.1.2 Where this protective measure is to be used as the sole protective measure (i.e. where a whole
installation or circuit is intended to consist entirely of equipment with double insulation or reinforced insulation),
it shall be verified that effective measures, for example by adequate supervision.
 
z
Can ADS be provided in the absence of a cpc. ?

Also:
412.1.2 Where this protective measure is to be used as the sole protective measure (i.e. where a whole
installation or circuit is intended to consist entirely of equipment with double insulation or reinforced insulation),
it shall be verified that effective measures, for example by adequate supervision.
We may be at cross purposes. 411.1 should clarify my point:

411 PROTECTIVE MEASURE: AUTOMATIC DISCONNECTION OF SUPPLY
411.1 General
...
Where this protective measure is applied, Class II equipment may also be used.
 
No class 2 in dwellings?

how many appliances or equipment in a dwelling are class 2 and are vastly more likely to be touched than a fitting screwed to the ceiling.


Just to clarify… I’m not saying everything has to be class 2…. Nor am I suggesting that this particular manufacturer only makes class 2 fittings.
Class 1 or class 2, they are designed and manufactured to industry standards, and if sold in UK…. They will be safe and fit for purpose…. If installed correctly according to manufacturers instructions.
 
No class 2 in dwellings?
I didn't actually say No class 2 in dwellings.

how many appliances or equipment in a dwelling are class 2 and are vastly more likely to be touched than a fitting screwed to the ceiling.
I wonder how many have fitted class 2 because of the lack of a cpc and would this be compliant ?
 
We may be at cross purposes. 411.1 should clarify my point:

411 PROTECTIVE MEASURE: AUTOMATIC DISCONNECTION OF SUPPLY
411.1 General
...
Where this protective measure is applied, Class II equipment may also be used.
Yes, my point was 412.1.2 Where this protective measure is to be used as the sole protective measure.
 

Reply to Class 2 light fitting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
302
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
874
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
849

Similar threads

The manufacturer has stuck a label on the baseplate, its clear to see. I don't know what instructions came with the fitting or what was written on...
2 3
Replies
37
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top