On a test & inspection today, I came across an older Wylex split load board that had been modified to add RCD protection for all circuits (see photo). The main switch was replaced with an RCD (despite there being room to add the second RCD to the left of the main switch). So a fault (or RCD test) on the LH bank of circuits trips both RCDs.
I'm inclined to code this as C3, since it defeats the object of trying to provide some discrimination, not necessarily potentially dangerous.
I'm wondering if others would be thinking this is an unapproved modification of a board, and perhaps should be a C2?
The EICR will be unsatisfactory anyway, there are other issues like holes in the front cover, an RFC with open circuit rN, some unearthed metal fittings, etc.
I'm inclined to code this as C3, since it defeats the object of trying to provide some discrimination, not necessarily potentially dangerous.
I'm wondering if others would be thinking this is an unapproved modification of a board, and perhaps should be a C2?
The EICR will be unsatisfactory anyway, there are other issues like holes in the front cover, an RFC with open circuit rN, some unearthed metal fittings, etc.