Code for no SPD on new build

newfutile

-
Arms
Supporter
I usually code no spd with no code or a C3.
However I have been sent to check compliance with BS 7671 on some new builds, there is no SPD present.

We usually say the date installed does not make a difference to coding but it does in a way.

The same may apply if Arc Fault Detection Device not installed in high rise flats or care homes.
 
TL;DR
Spd eicr code
As far as I’m aware, can the occupant still refuse an SPD, if they decide that they don’t need one?
Signed waiver after risk assessment?

Don’t know how that stands with a developer/ builder, As they are the customer, but not the final user.

new builds should have capacity, and even a cable already in for EV point…
 
As far as I’m aware, can the occupant still refuse an SPD, if they decide that they don’t need one?
Signed waiver after risk assessment?

Don’t know how that stands with a developer/ builder, As they are the customer, but not the final user.

new builds should have capacity, and even a cable already in for EV point…
its in a communal area which includes AOV door entry and emergency lighting.
i work for a housing association so we are the client
 
Gotcha.

I thought you’de been brought in as a 3rd party to check someone else’s job.


Should it have been specced beforehand whether to include SPDs?

I wouldn’t expect it needs it. There’s not a lot there to be damaged if a surge was to happen.
Not like thousands of pounds worth of consumer electronics going PFFFT!

Is “communal areas” classed as domestic or outwith that description?
 
its in a communal area which includes AOV door entry and emergency lighting.
i work for a housing association so we are the client
Regulation 443.4.1 requires protection against transient overvoltages to be provided where the consequence
caused by the overvoltage could result in:
(i) serious injury to, or loss of, human life
(ii) failure of a safety service, as defined in Part 2
(iii) significant financial or data loss.

I would have thought that applies to emergency lighting and smoke alarms.
 
Regulation 443.4.1 requires protection against transient overvoltages to be provided where the consequence
caused by the overvoltage could result in:
(i) serious injury to, or loss of, human life
(ii) failure of a safety service, as defined in Part 2
(iii) significant financial or data loss.

I would have thought that applies to emergency lighting and smoke alarms.
Point (ii) was removed in a corrigendum in 2023:

Indent (ii) of Regulation 443.4.1 has been removed. The term safety service, formerly included in Regulation 443.4.1 (ii), encompassed a wide range of systems. The provision, therefore, had unintended consequences for improvements to fire safety systems within installations.
 
Point (ii) was removed in a corrigendum in 2023:

Indent (ii) of Regulation 443.4.1 has been removed. The term safety service, formerly included in Regulation 443.4.1 (ii), encompassed a wide range of systems. The provision, therefore, had unintended consequences for improvements to fire safety systems within installations.
Thanks, I missed that corrigendum completely.

There is also BS 5839 series to consider.
 