A disagreement i've had yet again...
There is a workshop ring main with 4 double sockets and a indicated switched FCU feeding a single socket - this socket is wired in 1.5mm where the rest of the ring is 2.5mm 32A.
The spur from the FCU is roughly 1meter.
Now i know the answer to this, but had a disagreement with an electrician? (over the phone) today as he is rectifying the codes on a unsatisfactory EICR i've just completed.
Now the question is for you guys, or maybe a trainee / apprentice ... C1, C2, C3, FI or no code ?
I haven't a clue who is doing the code corrections and whether he is an electrician or not, but, if he is its scary that people are so out of touch with the regs and have no or little understand of the codes. I realise codes are open to interpretation, but not on things as trivial as this.
There is a workshop ring main with 4 double sockets and a indicated switched FCU feeding a single socket - this socket is wired in 1.5mm where the rest of the ring is 2.5mm 32A.
The spur from the FCU is roughly 1meter.
Now i know the answer to this, but had a disagreement with an electrician? (over the phone) today as he is rectifying the codes on a unsatisfactory EICR i've just completed.
Now the question is for you guys, or maybe a trainee / apprentice ... C1, C2, C3, FI or no code ?
I haven't a clue who is doing the code corrections and whether he is an electrician or not, but, if he is its scary that people are so out of touch with the regs and have no or little understand of the codes. I realise codes are open to interpretation, but not on things as trivial as this.