Here I would query the "long duration" of a small overload. MCB curves allow for trip times from about an hour all the way down to the 10ms or so magnetic trip time.

To me a long duration is then something lasting longer than an hour that won't trip the MCB but is above the ratings. For any sane use of a shower I doubt it would be on for more then 30 minutes once or twice a day, so unless you already see signs of thermal stress, I would say C3 as poor design but not ever likely to be running for more than the max design trip-time of a MCB.

We allow diversity on cookers for rating the cable and MCB on a similar basis, it is in that region of overload only for several minute but below the MCB's thermal time-curve until the thermostats start cycling and the cooker demand drops down.

Had it been something like an immersion heater that could well be on for hours at a time then I would think it merits C2.
 
Here I would query the "long duration" of a small overload. MCB curves allow for trip times from about an hour all the way down to the 10ms or so magnetic trip time.

To me a long duration is then something lasting longer than an hour that won't trip the MCB but is above the ratings. For any sane use of a shower I doubt it would be on for more then 30 minutes once or twice a day, so unless you already see signs of thermal stress, I would say C3 as poor design but not ever likely to be running for more than the max design trip-time of a MCB.

We allow diversity on cookers for rating the cable and MCB on a similar basis, it is in that region of overload only for several minute but below the MCB's thermal time-curve until the thermostats start cycling and the cooker demand drops down.

Had it been something like an immersion heater that could well be on for hours at a time then I would think it merits C2.
I guess that's reasonable thanks for your input.
 
In the real world, I still think that if a clamp meter was put on the supply to this shower, you'd find that the actual current is considerably less than the simple theoretical one.
I'll try to remember to do this when I return for remedials, it'll be interesting to see what the actual current drawn is.

Well, I'm settled on a C3 now, which will delight the tight fisted old landlord no end, as he won't have to shell out for a new CU.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Warwickshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Coding question - 8.5kw shower, B32
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
34

Thread Tags

Advert

Thread statistics

Created
Pretty Mouth,
Last reply from
Pretty Mouth,
Replies
34
Views
6,250

Advert

TrueNAS JBOD Storage Server

Back
Top