hi everyone, hope you can help. im currently installing a small submain to supply a DB which is then supplying a cctv power supply. there is a new lucy 25amp cutout in an external cabinet which has recently been installed prior to my work being carried out, when i have carried out work which involves a lucy cutout there has always been an earth block already fixed onto the side of the neutral block. The one i am working from just has concentric cable to Live and to the CEN block.
So i am asking if i require an earth rod to a new earth block, or bring an earth cable from the neutral block to an earth block? I would put a rod in myself but i just want to be 100% sure.

thanks
 
What sort of overall installation are you working on?? Some sort of Highways installation??

Generally, If we are talking about a ''Submain'' from a PME/TNC-S supplied main distribution board, then you can't go making further N-E connections as you go. A PME connection is made ONCE at origin, the main distribution board should then be distributing sub-mains as TN-S, where the earth requires a separate earthing block (EMT).
 
What sort of overall installation are you working on?? Some sort of Highways installation??

Generally, If we are talking about a ''Submain'' from a PME/TNC-S supplied main distribution board, then you can't go making further N-E connections as you go. A PME connection is made ONCE at origin, the main distribution board should then be distributing sub-mains as TN-S, or TN which will require a TT earth at the load end of the distributed sub-main.
well...i thought it was clear about creating TN-C....
 
I'm just as confused now!! lol!! The OP starts of by saying he has a concentric sub-main cable, then changes to saying he has a 3 core sub-main cable?? Either way if this is an overall PME supplied installation you can't go making numerous PME N-E connections. So i'm not quite understanding why these so-called sub-main lucy heads, are generally provided with CEN blocks, which to my mind, would make them unsuitable for sub-main installations (unless the N-E connection is via a removable sliding link to enable, either or TN-S / TNC-S supply), they are designed for being placed at the origin of a DNO supply.
 
I'm just as confused now!! lol!! The OP starts of by saying he has a concentric sub-main cable, then changes to saying he has a 3 core sub-main cable?? Either way if this is an overall PME supplied installation you can't go making numerous PME N-E connections. So i'm not quite understanding why these so-called sub-main lucy heads, are generally provided with CEN blocks, which to my mind, would make them unsuitable for sub-main installations (unless the N-E connection is via a removable sliding link to enable, either or TN-S / TNC-S supply), they are designed for being placed at the origin of a DNO supply.

nope , i understand the post as this ;

a feeder pillar with 25a pme dno cut-out with combined N & E terminal , supplied by pvc concentric cable

then a 3 core submains is ran from this to the cctv switchgear.

at no point is the N & E combined beyond the dno cut-out which is perfectly acceptable.
there is no removable earth link as the cut-out is too physically small for such a feature
as per the picture in this link..........

http://www.lucyswitchgear.com/media/25982/tds slf double pole cne.pdf

as for glenns comments regarding verifying its actually pme , i can absolutely guarantee that the dno will not install a TT supply within a metal enclosure in a public location , for reasons that are blatantly obvious.
;-)
 
nope , i understand the post as this ;

a feeder pillar with 25a pme dno cut-out with combined N & E terminal , supplied by pvc concentric cable

then a 3 core submains is ran from this to the cctv switchgear.

at no point is the N & E combined beyond the dno cut-out which is perfectly acceptable.
there is no removable earth link as the cut-out is too physically small for such a feature
as per the picture in this link..........

http://www.lucyswitchgear.com/media/25982/tds slf double pole cne.pdf

as for glenns comments regarding verifying its actually pme , i can absolutely guarantee that the dno will not install a TT supply within a metal enclosure in a public location , for reasons that are blatantly obvious.
;-)

Okay, that makes far more sense than what i made of it, before my second morning cup of coffee!! ...lol!!

I think the confusion here is the term ''sub-main distribution''. If these DNO Lucy cut-out's are direct from the DNO's supply, then they aren't classed as sub-mains as such. I take it that these DNO feeder pillars, as they are being called, don't have a main supply in and then subdivided off via these lucy cut-outs??
 
the mis understanding is probably from the OP's discription , but any wiring after the cut-out ( eg tails or a swa submain ) will be on the consumers side of the installation.

the feeder pillar itself remains the property of the local authority , only the cutout is owned by the dno.
i've looked for a picture to help describe the set-up but found nowt , i'll break into 1 later and take a photo ( i still have a set of master keys ) ;-)
 
the mis understanding is probably from the OP's discription , but any wiring after the cut-out ( eg tails or a swa submain ) will be on the consumers side of the installation.

the feeder pillar itself remains the property of the local authority , only the cutout is owned by the dno.
i've looked for a picture to help describe the set-up but found nowt , i'll break into 1 later and take a photo ( i still have a set of master keys ) ;-)

Now that would be interesting, i'll look forward seeing those feeder pillar pic's!!

I don't think you'd be able to directly terminate a SWA into those Lucy cut-outs, the gland plates are in two halves, one half being integral with the cover plate!!
 

Reply to combined earth + neutral cutout in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
716

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top