OP
hodgey1972
Thanks guys, appriciate the input
Discuss commercial dsitribution board change leaving existing circuits non rcd protected in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I would argue that in the case of a board change where the OCPD is changed then as long as you have not made the circuit any less safe then you can treat it still as an existing circuit wired to a previous edition of the regulations, I cannot see why changing a board should make you bring any circuit up to standards just because the OCPD has different characteristics, as long as the circuit isn't a code 1 for any reason then I would treat as existing.
This is my opinion not a regulation, I believe you have to ensure that any alteration or edition must comply to current regulations where this is in the form of altering or adding to the circuit then yes! your work should follow current regulation but where the alteration is not the circuit but the actual device protecting the circuit then as long as it doesn't afford any less protection for the circuit than the previous device it should be the case you don't have to bring the whole circuit up to regulations.
not sure if i have misunderstood here..
by changing the fuse board- you work has to comply to the current regs- so if existing circuits require rcd protection- then you must protect them by rcd
you can't just change to a 16ed fuse board and then only rcbo a new circuit you have installed!
or am I reading wrong here lol
The requirement, is that your work must comply with BS7671.
There is no requirement for you to upgrade existing circuits.
Also there is only a requirement for certain circuits to be provided RCD protection, such circuits as those of a location, containing a bath or shower or socket circuits in agricultural/horticultural installations.
Such as?and the others...
Reply to commercial dsitribution board change leaving existing circuits non rcd protected in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net