I was going to say the samething mate as the tray is mechanical support for the cable.if it's on top of the tray, tie raps are fine, as the cable is supported by the tray, not the ties
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss commercial fire alarm in the Electrician Talk | All Countries area at ElectriciansForums.net
I was going to say the samething mate as the tray is mechanical support for the cable.if it's on top of the tray, tie raps are fine, as the cable is supported by the tray, not the ties
Fuse spurs to Fire alarm panels need to be lockable, double pole switched fuse spurs.
They are readily available from electrical wholesalers. They are basically premade mk em secret switches in red metal casing.
Also good design to meet DDA is siren/strobe units in all toilets as ammended BS5839, most deaf people don`t used disabled toilets. If this building is large you may considor paging system for disabled, good system by scope. hope this helps
accord, lockable double poled switch fused spur. agreed by bsi by Colin Todd for bs5839 2002. hence mk and other manufactures produced such an item.
if it's on top of the tray, tie raps are fine, as the cable is supported by the tray, not the ties
I was going to say the samething mate as the tray is mechanical support for the cable.
accord, lockable double poled switch fused spur. agreed by bsi by Colin Todd for bs5839 2002. hence mk and other manufactures produced such an item.
No, not strictly true.
BS 5839-1:2002, Section 2, Clause 25.2 applies.
It states that every connection to the LV mains supply should be labelled, double pole isolating and *should* be out of reach of unauthorised persons, or operable by means of a special tool.
Time and again, it has been clarified all over the industry that a double pole, non-switched fused spur, with a screw in fuse holder is adequate.
Nowhere at all does it state that it needs to be "lockable" - I've just been through both 2002 and the 2008 A2. Yes, sadly, I can be that ----.
Please contact BSI house for clarification, This is also requirement of BAFE.
This information was confirmed to us by the co/writer of standard Colin Todd BSI House
Seems to be the old case of "must" and "should" and "interpretation"
To me special tool = some sort of key even if this is a grid keyswitch
With regards to BSI and Mr Todd as the writer if they prefer a particular method this does not preclude other solutions that may be interpreted from their and his publications
Now finalised, BSI state double pole isolator local to the panel, for service and commissioning purposes, which is protected from unauthorised or accidentel disconnection via an enclosure or which is lockable. A simple recommendation is to fit readily made mk or crabtree purpose made lockable fused spurs.
BAFE and LPC both confirm the above stating unswitched fused spurs would be deemed as failure to comply.
Morley/Notifier, Kentec, Haes & Advanced all state within their manuals to install local double pole isolators, they all confirm the easy solution is to install mk.
C-Tec state since 2002 all new manuals state lockable double pole switched fused spur.
[/QUOTE]FM companies (jack of all trades servicing companies) should become members of BAFE or LPC before making such rash comments on BSi standards
Will you please go and get professional advice from the relevent bodies or stick with NACOSS
Again I suggest you phone the relivent BSI & BAFE and inquire then we will continue this debate