communal lighting , contactor | Page 2 | on ElectriciansForums
Discuss communal lighting , contactor in the UK Electrical Forum area at ElectriciansForums.net
G
glasgospark
got a 240v ac set up for communal lighting in a small block of flats ,
call out was that outside lights not working , the contactor has 25mm incomer from db1 and 25mm outgoing to db2
incoming side also has 1.5mm t&e.
i cant seem to find the operating device for the contactor any suggestions ??
dusk-dawn pir ?
the25mm perm feed and neutral are in the top front terminals of the contactor , then theres the 1.5mm cables at the back of the contactor l-n ,then the load at the bottom ,
the 1.5 is obviously the L-N for the photocell but how does the photocell then make the switch to pull in the contactor
The photocell is usually just a single pole switch, permanent live in and switched live out to A1 or A2 on the contactor.
25mm is a helluva large supply for '1 2d 28w fitting', are you sure that's all that's being supplied?
the incomers are huge i know , its feeding the 2d and 8 70w son lamps
- - - Updated - - -
wouldnt the photocell require neutral to operate ??
Reply to communal lighting , contactor in the UK Electrical Forum area at ElectriciansForums.net