got a 240v ac set up for communal lighting in a small block of flats ,
call out was that outside lights not working , the contactor has 25mm incomer from db1 and 25mm outgoing to db2
incoming side also has 1.5mm t&e.
i cant seem to find the operating device for the contactor any suggestions ??
dusk-dawn pir ?
Maybe the load was larger and got trimmed or maybe as Mick says it's future provision but it's a large provision so I'm sure there'd be a definate reason behind it.
Bottom line is regardless of tail sizes it's a very simple circuit. PIR operates the contactor, contactor switches power to DB and brings in the lights. There's numerous ways the wiring could be physically laid out same as there's several ways to cable a normal domestic lighting circuit.
.....personally i cant see the need for contactor
Pleeeeese don't remove the contactor. The SON lighing load is probably far from linear plus there's start currents to consider, I doubt the PIR is rated to switch the load directly. Just fault-find the existing setup and fix it. If you alter the circuit make sure you have a design that you know is viable because it will be your responsibility if you do.
i have bypassed the contactor for now , feeding the db from a 20a mcb with 2.5 t&e untill i can get to photocell ,
its 10meters up
Every photocell I've come across needs a live neutral and switch wire.
is there a slid lock fuse or something that is in circuit to switch the d/b?
as it was quite common back in the day to fuse the control circuit down using such methods.
start there and look to see if the photocell has had it