This is quite rubbish, and very simple, but I'll put this up as it was a learning experience.
4 core 4mm SWA, already poked through a plasterboard wall and cut to approximate length, I had to clip it to the wall and terminate in a metal 3P DB. There was an additional 6mm CPC, as the aim was to reduce Zs on the dist board circuits as low as possible.
I was told to cable-tie the CPC to the SWA rather than clip it to the wall. I was told to use a closed 20mm rubber grommet to pass the CPC into the metal DB, rather than use a stuffing gland. The environmental conditions are not onerous at all. The cable is not near/over an escape route, so I was happy to use plastic clips. The run is level, the clips are 400mm apart, as per table D1 in the OSG. Bend radius is about 12cm (minimum ~9cm, table D5).
If I were to do the same job again, with the same limitations on fixing materials, I would measure the distance between the two 90 degree bends and work out how to space the clips evenly (making sure they were spaced <400mm apart), I would try to get the SWA more perpendicular to the top of the DB before making it off, and I would put the cable-ties on the other way round so the knobble was at the top out of the way.
This task (which took me over an hour, including terminating the SWA in the board) taught me that there's quite a lot to think about, even for a seemingly simple task. I know this won't win any medals, but I thought I'd share and I'd welcome any comments.