Nicebloke

When unable to carry out a Zs test on a lighting circuit (large/heavy chandelier type lighting), then the R1+R2 + Ze measurements are instead used and this is noted, but is it the norm to still write this value in the Zs box on the schedule of test results or just in the notes. I ask because technically a Zs test hasn't been conducted, and the R1+R2 + Ze calculated isn't necessarily going to be the same as an actual Zs test?
 
R1+R2 added to Ze is a worst case,a direct Zs may include parallel earth paths and would tend to make it lower,if the R1+R2 calculation is within limits,the true Zs will almost certainly make it better in the real world
 

Reply to Completing Zs box on schedule of test results in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top