Hi there,

I'm planning a shed supply project in order to get my part p...

The concrete shed is going to have 3 double sockets and 4 strip lights. There is a spare way in the house CU.
The shed is roughly 50 metres along from the house CU.

Here is my plan...
From the spare way in the CU, 6mm SWA cable fixed to the garden fence (or underground) on a 40A RCBO supplying a garage consumer unit with 30mA RCD. From here, a 1mm cabled radial lighting circuit on 6A breaker and a ring circuit for the sockets using 2.5/1.5mm cable on a 30A breaker...


Does this sound any good?!?!

Willy:D
 
Hi

Theres a cracking little volt-drop calculator on the TLC-Direct website here Voltage Drop Calculator

I personally would use a 10mm 2 core SWA fed from the consumer unit from a 40A MCB (no rcd required due to earthed armour). Earth the armour at the house consumer unit end, but NOT at the garage end.

Then use an RCD protected consumer unit in the garage and install an earth rod at the garage end to make the garage a seperate equipotential zone.


nrgmark
 
Hi

Theres a cracking little volt-drop calculator on the TLC-Direct website here Voltage Drop Calculator

I personally would use a 10mm 2 core SWA fed from the consumer unit from a 40A MCB (no rcd required due to earthed armour). Earth the armour at the house consumer unit end, but NOT at the garage end.

Then use an RCD protected consumer unit in the garage and install an earth rod at the garage end to make the garage a seperate equipotential zone.


nrgmark

why does he have to put a separate earth to the garage?
 
@Hawk81

Well yes, he could use a 10mm 3 core SWA and extend the house equipotential zone. I am just saying what I would do personally, based on the fact that the NIC guy who comes and inspects me prefers that outbuildings have their own seperate equipotential zone. But I do find that a few of them have conflicting ideas about things.


nrgmark
 
if PME sorry TN-C-S supply then you have to provide seperate earth for garage ie rod and RCD


re yesterdays post
have contacted NIC tech help and verdict is to use rod and RCD at garage end
this is to prevent the extension of the equipotential zone and any problems bonding now or in future
and is to comply with the esqc regs which i wiil check and post back findings
 
re yesterdays post
have contacted NIC tech help and verdict is to use rod and RCD at garage end
this is to prevent the extension of the equipotential zone and any problems bonding now or in future
and is to comply with the esqc regs which i wiil check and post back findings

The NIC need to read GN8 and probably the Regs while they're at it.

They also need to realise that they don't make the rules.:)

They are annoying when they come up with their own regulations that are in contradiction with BS7671:mad:
 

Reply to Concrete shed supply... in the Australia area at ElectriciansForums.net

Similar threads

You should have no problems with what you want but even if you install conduit the cable still needs to be UF cable which is approved for under...
Replies
1
Views
568
  • Question
I've elected to undelete this thread because the reason given by the OP when he deleted it was 'Unhelpful' which I think in this case translates...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks