Hi Lads doing an insulation resistance test and getting a reading of 324.5 ohms on a ring main does anything below 500 ohms need to be rewired?

Thanks
 
When doing an IR test the scale should be in Meg ohms not ohms.
Are you using the correct instruement for the test.
 
I have had it before where one of the sockets was the problem, sounds like some fault finding is needed (whoopee). Assuming you are testing it right and everything is definately unplugged/disconnected, but it doesn't mean rewiring it anyway, maybe just a section of it
 
Circuits up to 500V must have a minimum insulation resistance of 1.0 Meg ohms when tested at 500v dc with all current using equipment disconnected. 612.3.2
 
It's not quite as simple as "<1M Ohm = Rewire" - there are other factors which need to be taken into consideration which could be causing the low reading, such as equipment (eg surge protector, heater, tv signal booster, anything with a neon on it) plugged in or connected, or even just a poor termination.

It's worth doing some further investigation such as hunting around for hidden equipment (try the loft),and/or splitting the ring and testing each leg, before you go diving in and rewiring the whole property - that kind of behaviour can earn you an undesirable reputation.
 
It's not quite as simple as "<1M Ohm = Rewire" - there are other factors which need to be taken into consideration which could be causing the low reading, such as equipment (eg surge protector, heater, tv signal booster, anything with a neon on it) plugged in or connected, or even just a poor termination.

It's worth doing some further investigation such as hunting around for hidden equipment (try the loft),and/or splitting the ring and testing each leg, before you go diving in and rewiring the whole property - that kind of behaviour can earn you an undesirable reputation.


How very very true


Chris
 
i used to work with a guy that could tell by just looking at the board with the cover still on whether it needed re wiring or not. what a clever guy, made me wonder why i had spent good money on a tester with qualities like that :confused: he always seemed to get the full rewire after as well maybe it was due to his shock tactics with what might happen to the wiring etc without a new board and re wire.
 
question posed to the OP needs to be answered by him- was your reading in M ohms, i.e. million ohms or in Ohms ? - extremly important m8 !
 
Thanks guys. This house is a void and has no one living in it. Doing the test on my multi meter at 500 volt and its in meg ohms,just don't feel very confident and don't want to bull**** anyone just an honest report
 
m8- megger testers read up to 299 mo, my 1652b to 500 mo. (500,000,000 ) ohms. your reading at that level is very good. 1mo is the basic pass !! but i would recommend investigation at that level !!
 
i used to work with a guy that could tell by just looking at the board with the cover still on whether it needed re wiring or not. what a clever guy, made me wonder why i had spent good money on a tester with qualities like that :confused: he always seemed to get the full rewire after as well maybe it was due to his shock tactics with what might happen to the wiring etc without a new board and re wire.

Has he appeared on rogue traders or has nobody caught up with him
 

Reply to confused on testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

Hi Dave thanks for the info I revisited the premises to change a cooker switch and redone the test from the MET with MET disconnected from DB...
Replies
16
Views
1K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top