My purpose E54 is not to start another argument on this but simply to provide a balanced opinion as I fundamentally disagree with your views on small TT systems in the UK....(as you know).....
FYI my allotment is on weald clay,and I can assure you the ground has not frozen more than 6 inches down in very severe weather...I am in the south east and accept the situation may be different in the north...although I doubt it would freeze even half way down a standard UK rod even there.
In 30 years I have never heard of a problem or safety related incident on a UK TT system installed in accordance with Bs 7671 which could be attributed to the standards of Bs 7671 being inadequate...and I base my opinions on that.
I most certainly disagree with your view on TT systems too, especially your total acceptance of 200 ohms being suitable/adequate, based purely on what is written in BS7671. That section of the Reg's is clearly in need of revision. Iv'e always stated that getting a good Ra value on a domestic installation can sometimes be an expensive exercise. But in many cases the use of 3 or more rods coupled together for depth can bring you sub 10 ohm Ra values. Which WILL give a form of protection, even if not meeting disconnection times, for when that RCD(s) fails. I have also stated many times in this forum that whenever possible a PME conversion is always going to be the better route to go in the UK!!
Ground freezing in the UK has always been a problem, even in Essex where i spent most of my time in UK. Just go ask groundwork's companies, i would imagine it's even more common for water retention type soils, the further North you go... Same goes for drying of general soils, especially in free draining type soils, even in what UK call summers these days...lol!! And remember, you only have a metre rod, ...''Any'' reduction in resistivity caused by freezing or drying of the soil, is going to have grave affects on the stability and Ra value of that rod...
I'm glad you mentioned previously about the ''UK's standard'' 1 metre rods... I'm being honest, when i tell you, that i've never seen a 1m rod in my entire working career, even when i was training/working in the UK!! I have seen 1m extension rods threaded one end only. The smallest earth rods i've seen or worked with have been 2.4m 5/8''. Normally and the vast majority of the rods i have used on my projects are 3.1m 3/4'' , and i am talking literary thousands of them over the years, several hundred on my present project alone...
To be totally honest with you, those 1m 3/8'' rods should be discontinued/scraped as ''unfit for purpose'' ...I've seen bigger earth test kit electrodes than those totally usless things!!
One thing i will say about your 1m rods ....never on god's earth will a 1m 3/8'' or 5/8'' rod give you a stable TT earth, in a general/typical soil condition, but you may just be lucky in a salt marshland location... lol!!!
I base my opinions on what i've learnt over the years and the early mistakes i've made and seen. along with the many projects, where that experience was put into practice. It is 100% NOT based on the standards of BS7671. Maybe a better standard to follow in the UK, would be that found in the ''Lightning Protection'' standard , (can't remember the BS/EN number)