@Simon Linton How do you plan to provide the earth?
First of all, physically at the box you have chosen.
Secondly, I guess you are using the SWA? will the steel armour meet the requirements? Or are you TT'ing the distant end?
 
Fair enough, but wouldn't you use a cable which allows you to keep the cpc the same size for the whole run?
I'd certainly have a little think about whether it mattered or not. In many cases it won't, provided that the cpc meets the minimum requirements over the whole length of the circuit. If the T&E runs into the board, it'll be obvious that the circuit has more than one cable type. If someone was to insert a piece of T&E into the middle of a run of SWA, I'd be less likely to approve.
 
Why do you want to extend SWA with T&E?
I was taught that you should always extend a wiring system with either the same type or another type which has equal or better protection.
The SWA goes to the basement inside the house so the 6mm twin and earth will be all be indoors and clipped back to the house consumer unit.
 

Reply to Connecting SWA to Twin and Earth cable? in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
889
Sounds more positive.
Replies
8
Views
613

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top