connections of cpc | on ElectriciansForums

Discuss connections of cpc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Mar 15, 2013
Messages
93
Reaction score
2
Location
gloucetser
hi,

Testing a job at the moment and a couple of DB have all there CPC connected in the trunking instead of the DB. There is a earh bar within the metal trunking but due to the trunking full of cables, unabale to gain access to the CPC. Due poor access to the CPC ive made a report on that but is the earh bar in the trunking ok?

Thanks dave
 
Yh the installation is in a poor way, Looks like the CPC wasnt long enough for a new board change so all connection be made in the metal trunking with guar dthe cpcs.
 
I would say that it isn't acceptable to have the earth bar in the trunking. I am not saying it is against the regs, but my concern would be the possibility of line and neutral conductors chaffing against the earth if the trunking is tightly packed as you say. I would extend them in to the DB somehow. How you do this will be down to you, as you can see the set up and not us. I would code it C3, it isn't C2 cos if something does chaff through it will trip something out i would hope.

Cheers…………Howard
 
I would say that as well as being poor installation practice, it I think go against BS 7671, where the earth bar is after all acting as a junction box/enclosure, and with other circuits running adjacent to it in the trunking is a n0 no, thats what I think anyway others may have different ideas.
Pete999
 
Im still only learning and personally i wouldnt terminate cpcs in the trunking on account of bad practice, but, on some installs the met isnt always in the d/b ie close to the meter. My question is (if not chaffing any cables) is there any lack of fault protection here? Id definitely snag it for lack access for testing and inspecting though :)
 
If were talking about a full metal containment system installation here, there shouldn't be any need for individual circuit CPC's, the metal containment itself is the installations CPC!!
 
Old school stuff and its still found here and there, agree with eng 54 about the trunking being an earth but personally never liked it

Explain to me what you don't like about a full metal containment system being the CPC for the circuits it's supplying??

Nothing old school about it, apart from being used for far more years than anyone here can remember, ....Why, because it works and works better than containment filling individual circuit CPC's!! The project i'm working on now, along with every other major project i've worked with, that has extensive metal containment systems throughout, have never included separate circuit CPC's.

I'd put bet's on, that the Zs values that i'm used to seeing, are far superior than anything you would typically expect to see!!
 
I'm a big fan of full metal containment, during my apprenticeship we ran metal containment accross 4 floors and used conduit etc as cpc. No problems whatsoever! Biggest problem we come accross now is people adding extensions etc to these circuits but not continuing the earth path correctly
 
I'm a big fan of full metal containment, during my apprenticeship we ran metal containment accross 4 floors and used conduit etc as cpc. No problems whatsoever! Biggest problem we come accross now is people adding extensions etc to these circuits but not continuing the earth path correctly

They are called electrical trainee's Joe, and wouldn't know any different, let alone be able to work on any metallic containment systems!!
 
Are there any manufactures data on the CSA of their containment?

Here you go.....

The first 2 tables are for conduit and trunking....

[ElectriciansForums.net] connections of cpc
SWA CSA of Armour.pdf (58.0 KB, 907 views)
 
Last edited by a moderator:

Reply to connections of cpc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

I see no issue with this, it sounds like a relatively normal installation. The use of insulated and sheathed cables inside steel trunking is a...
Replies
5
Views
257
davesparks
D
I guess my last post was even less direct than intended.
    • Like
Replies
11
Views
657
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top