Explain to me what you don't like about a full metal containment system being the CPC for the circuits it's supplying??
Nothing old school about it, apart from being used for far more years than anyone here can remember, ....Why, because it works and works better than containment filling individual circuit CPC's!! The project i'm working on now, along with every other major project i've worked with, that has extensive metal containment systems throughout, have never included separate circuit CPC's.
I'd put bet's on, that the Zs values that i'm used to seeing, are far superior than anything you would typically expect to see!!
Well i can show you hundreds if not thousands of metal containment systems that are nearly as old as me, that will still give superior Zs values without a single separate CPC in sight!!
It has nothing to do with the perfect world scenario you imply, but everything to do with installation tradesmen installing metal containment systems correctly/properly. No, junctions between trunking and conduit do not cause problematic areas if they are made correctly in the first place. I bet you have never seen a high current metal containment system test set that can/will prove every metal to metal connection on the system, section by section!! You also do not base an installation method on what may or may not happen in the future, or on incompetent persons making non compliant alterations. There has been no better rewirable containment system (depending on the environment) than metal containment systems. They provide excellent mechanical protection, electrical protection (Zs values), lifespan expectancy, and a good few more real advantages over other containment systems to boot.
Seeing as many electricians these day's have never installed and i think i would be right in saying are not even capable of installing a metal containment system, they would know no better. Basically it comes down to asking, what fool would fill up a metal conduit with CPC's, when the containment itself is far bloody superior than the combined separate CPC's??
As i have stated previously, i have NEVER installed separate CPC's on ANY of the the projects i've been involved with ''Including'' my present project, and more importantly it has never been requested/required in any of the contract electrical specifications. Obviously you never electricians think you know better than us, ...but i put it to you, that past T&E, SWA, plastic containments and the like, you know very little!! And i'm not blaming the individuals, i put the blame firmly into the consistant lowering of our industries education standards....
Couldn't disagree with you more, a metal conduit system that has been installed and erected correctly by skilled tradesmen, will not decrease in reliability. I was brought up, or should i say dragged up on industrial metal containment systems, never seen one go bad, except where environmental conditions hadn't been taken into account, or the environmental useage of the area's conditions had changed. As stated previously, any signs of suspect joints and/or connections will show up like a sore thumb when initially tested with a high current ohm meter.
Not sure what you're saying here, are you saying that metal containment should be restricted to X amount of screwed connections?? That'll be a new one on me...
Why fill say a 20mm conduit system carrying maybe 3 circuits with 3 unnecessary CPC's?? It was never necessary in the past and it's not necessary now!! You're going to have to go some, to lose the equivalent of 10mm of copper on a 20mm conduit system. Never installed a CPC in metal containment and have no intention of ever doing so. ....Money straight down the drain!! ... lol!!
for godsake dont knock eng or he'll turn on u
lol
youre totally missing the point
certain circumstances steel conduit and trunking deteriate
i wouldn't rely on it in many situations in normal run of the mill jobs, rust does get in, that's the nature of steel
youre comment on not allowing for future alterations is short sighted to say the least
but hey ho
One has to be pragmatic - no equipment, material or technique is infallible. If everything is in good order then I agree that metal containment is a durable and effective CPC. But electrical systems erected commercially to a realistic budget and subjected to normal non-domestic usage, are likely to contain imperfections in cables, containment, switchgear and accessories. Some of those will be deterioration of weak spots created during installation, some will be random accidental damage, some deterioration due to age. Amongst them will be loose and high resistance joints in containment.
You could say that 99.99% of all metal containment systems will fall outside of domestic usage!!
Yes, you may well get some weakness in a few screwed connections etc, during installation but again, they will show up like a sore thumb under high current testing. As for random accidental damage during the life of the installation, one would expect that any damage to an electrical containment system would be corrected, ...again by skilled electricians..
In certain circumstances, such as the long tortuous conduit runs I described, adding a copper CPC could provide a worthwhile increase in CPC integrity, justifying its modest cost. In others, such as multiply-interconnected trunking grids, I am fully in agreement that adding a cable would serve no useful purpose either to decrease impedance or increase reliability.
On long tortuous conduit runs the size of the conductors would probably need to increase, and possibly the size of the conduit to accommodate the larger conductor sizes. But again, you would really need to go some, before that 10mm or more of equivalent copper conductor would be lost or need reinforcing by far smaller separate CPC's...
I'm not missing the point at all, metal containment systems do NOT require/need separate CPC's.
As i've indicated previously, if a metal containment system has been skillfully erected, using the proprietary conductive sealing paste to all screwed connections and the proprietary zinc paint to any exposed thread on a system suitable for the environment it is installed within, severe deterioration should not be a problem
Totally agree with that
Allowance for future additions and alterations, is not afforded to individual circuit conduit runs, that is normally afforded to DB's and the like. Start going down those lines and the installation is going to get very expensive very quickly. With trunking, you have in most instances, an inherent means of easily accommodating additions and alterations. Just wondering how you allow for incompetent persons undertaking any such work in the future
Most sites that sparks go to in the private sector don't have an unlimited budget and invariably additional circuits are required either when the client moves in or maybe a new tenant takes over the space, so a certain amount of additional capacity is always good. Invariable, most times sparks are asked to install additional circuits it would seem to be a case of "oh, one extra circuit won't hurt", obviously this can have a cumulative effect. It would be lovely to start again but economics generally don't allow such a luxury.
Further, i personally i haven't used solid core single cables in conduit, they are just not suitable or fit for purpose, being pulled into tube as far as i'm concerned, even less so when additional cables are pulled into an existing conduit system, stranded cables are by far, more accommodating all round!! I don't allow inspection bends and Tee's either, those bloody things rip cable insulation to shreds!!
Yes, some metallic conduit systems have been erected in unsuitable environmental conditions, and may well prematurely deteriorate. But then surely that installation would need to be replaced rather than try to fluff around with it, while still deteriorating further??