Customer: my electrics keep tripping after you did your work
Kent: that's because I didn't test ccts properly and now it will cost anything up to ÂŁ2000 to stop it tripping. Hell, you may need a full rewire.
Customer: so are my electrics unsafe?
Kent: yeah probably.... Dunno really.

Not the best way to approach business.

If you are upgrading from a possibly fine 3036 board to a RCD board then the new DB will pick up on faults that the 3036 would have not have done. Also as others have mentioned Zs maximums have probably changed.. End to end on RFCs may be open, etc, etc...so you should insist on testing so both you and the client know where you are. It would be really unprofessional to turn a ÂŁ400 job into a ÂŁ2400 job just so the client can have no nuisance tripping.

There is nothing in the regs saying an EICR is mandatory prior to a board change, but it is 100% a better option. As a bare minimum do some Zs tests and a global IR test, and warn customer of possible extras upon full testing.
 
Those who spout on about EICR's before a CU change are talking rubbish. Yes,in an ideal world. But consider that a full EICR on say a 3 bed semi is likely to take at least half a day. Most CU changes are a request for a quote,NOT just go ahead and do whatever is required,so you are going to spend half a day doing a pre-quote survey for a job you might not even get?Yeah right.
In the real world that 'EICR' amounts to a check of earthing,bonding and a global IR test,and a general condition assessment.Most electricians can sum up whether there are likely to be any issues within ten minutes of arrival. The quote will then state that a full test will be carried out during the CU change and any other faults found will be at extra cost.
 
Those who spout on about EICR's before a CU change are talking rubbish. Yes,in an ideal world. But consider that a full EICR on say a 3 bed semi is likely to take at least half a day. Most CU changes are a request for a quote,NOT just go ahead and do whatever is required,so you are going to spend half a day doing a pre-quote survey for a job you might not even get?Yeah right.
In the real world that 'EICR' amounts to a check of earthing,bonding and a global IR test,and a general condition assessment.Most electricians can sum up whether there are likely to be any issues within ten minutes of arrival. The quote will then state that a full test will be carried out during the CU change and any other faults found will be at extra cost.

I agree with you. We would use our experience to make a judgement and check the vitals. I suppose it becomes different when someone who lacks in experience wants to do the replacement and does not carry out some basic upfront checks.
 
I agree with you. We would use our experience to make a judgement and check the vitals. I suppose it becomes different when someone who lacks in experience wants to do the replacement and does not carry out some basic upfront checks.

Which explains the abundance of 'CU change RCD wont stay in but I've done everything right' threads on here!
Of course upfront checks are vital before a CU change/Quote....but I'm fricked if I'm going to do a full EICR for nothing when I get a CU change quote request.
 
well said wirepuller experience is what is needed, i have said many times a few basic tests , work out when the original install was done as this will possibly highlight a shared neutral ,full test after the boards done an EIC at the end of the day when the boards changed and form filled in its basically a check list for you
 

Reply to Consumer Unit Change - EIC, MWC, ECR ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top