Dont change many consumer units, usually go ok but had one today that I did cheap for next door neighbour (Why is it always the ones you do cheap for friends and family that bite you). Anyway changed the board etc, all ok. Then came testing and obviously have various alterations in the last 40yrs, still had original wylex rewireable fuses.

I found Neutral ring missing - A socket had a neutral out.
Conservatory had two sockets, a light and an automatic window opener all spured off a spur in the kitchen with no grommets in the back box (Apparently done by an electrician)
One socket of two gang no neutral - just change face plate
One socket no neutral (Spur) - Just had to wago and put blank plate as obviously a junction box under the floor
There was some others as well.

Anyway in my haste to speed up testing I did insulation resistance with a couple of sockets off (I know stupid), when powered on RCD kept tripping if I removed socket neutrals it was fine. Finally tracked it down to a really tight socket in the kitchen that had a damaged neutral cable, managed to sort everything.

Started at 9.30, was running around in the dark finished about 8pm with everything ok, im totally shattered.

I am thinking of insisting on a full EICR before I do a consumer unit change again, at least you know what you are getting into mostly and you dont spend an entire evening trying to chase down issues as once you have changed the board and especially adding RCD's your kinda committed.

Just wondering do others do EICR beforehand or just wing it?

If you just wing it how often do you have issues?
 
I cost in a morning or afternoon, a week or so before the board change, to do pre-board change inspection and test: earthing, bonding, IR, ring continuity, check for borrowed neutrals, and either R1+R2 or Zs on every circuit. When I give my quote, I explain (in writing) that the quote is subject to the existing circuits meeting the minimum requirements of the Regs; if it's something I can quickly and easily fix during the pre-change checks I'm happy to do so. If there is plenty wrong, then I reschedule the board change for further into the future, and spend the day I booked for the board change doing fault-finding and rectification (either as a quote, but usually on an hourly rate). This has happened about 2 or 3 times, out of about 30 board changes, and the client has always been grateful for sorting things out and doing stuff properly.

In theory, if I do the checks and there's a lot to sort out which the client doesn't want to pay for, the client can cancel the board change and doesn't owe me anything. This has never happened though.

I don't like surprises. When I strip out an old board, I want to make sure, as best I can, that the day will go smoothly. :)
Spot on in my opinion that’s what I do. I don’t charge full whack to do an EICR and then say you need your consumer unit changed and then charge for that. In some cases you already know after visually inspecting property and board cover off that it needs upgrading. So I would do a small fee for pre inspection of property and then set an amount of £350 approximate based on standard property with 6/7 circuits for board change. I will inform customer that should I find any faults after board change I will charge per hour for fault finding. I don’t like the fact that ppl charge £150/£300 for EICR then charge another £350 for board change when you already know that the property needs upgrading prior to EICR
 
You do IR tests with all the cpcs isolated from each other and the earthing conductor? I test as I am connecting them.
Yes, you're right Westward, I had to think for a moment. The back of the new board would be up, with all the cables coming into the new unit. Then, I would do individual IR tests just before I connect up the earths to the earth bar.
 
Agree
People who do mains changes with impact drivers need there hands chopping off

done lot of work on social housing and number of times I go in and try to torque tighten all existing terminals but only to find been install by some tool with a impact and all screws rounded off
My number 1 thing that grinds my gears!
Yesssss!!! Same here I’m testing a lot and the amount of terminals which are rounded, tightened by Arnold Schwarzenegger is unbelievable even the fuse board covers grips my ---- use your hand tools so you can feel the tension simple
[automerge]1601666539[/automerge]
Yesssss!!! Same here I’m testing a lot and the amount of terminals which are rounded, tightened by Arnold Schwarzenegger is unbelievable even the fuse board covers grips my ---- use your hand tools so you can feel the tension simple
Another pet hate is the earths twisted together in single sleeving why like? Sleeve them individually easy solution is to do end to end at socket but I like the fuse board lol
 
Last edited:
Yes, you're right Westward, I had to think for a moment. The back of the new board would be up, with all the cables coming into the new unit. Then, I would do individual IR tests just before I connect up the earths to the earth bar.
You should connect the cpcs first.
 
If people are using 18v impact drivers to tighten down terminal screws something went wrong with the trade...
Exactly I’m normally a calm guy but some of the boards I’ve had to test recently really wind me up. And I never had a problem 7 years ago it’s only the recently installed boards which seem to be glued shut
 
I don't approve of his method but to be fair he seemed well in control of the driver and didn't seem to over do the terminals.
I suppose if you have an understanding of power tools then it’s fine one of my best mates does it with impact and I cringe every time I see/hear him at the consumer but to be fair he understands the torque it’s the ones who don’t have knowledge/experience that cause the problems anyhow I don’t like power tools at consumer
 
I suppose if you have an understanding of power tools then it’s fine one of my best mates does it with impact and I cringe every time I see/hear him at the consumer but to be fair he understands the torque it’s the ones who don’t have knowledge/experience that cause the problems anyhow I don’t like power tools at consumer

The drill/driver is used in that video is not an impact driver and can be set to exceptionally low torques. I've no idea what it was set at and whether or not those terminals were over/under tightened, but it's worth noting that they are very different tools.
 
The drill/driver is used in that video is not an impact driver and can be set to exceptionally low torques. I've no idea what it was set at and whether or not those terminals were over/under tightened, but it's worth noting that they are very different tools.
Doesn’t matter shudn be using them unless like @telectrix just posted then that’s the exception “HAND TOOLS ONLY”
 
The drill/driver is used in that video is not an impact driver and can be set to exceptionally low torques. I've no idea what it was set at and whether or not those terminals were over/under tightened, but it's worth noting that they are very different tools.
What
The drill/driver is used in that video is not an impact driver and can be set to exceptionally low torques. I've no idea what it was set at and whether or not those terminals were over/under tightened, but it's worth noting that they are very different tools.
what do you use mate? Drill/driver is it?
[automerge]1601669683[/automerge]
Drill drivers can be set to exceptionally low torques - often so low that it wouldn't be considered much more than hand tight.

Having said that, I just looked at the video again and note that it is indeed an impact driver :tearsofjoy:
??
 

Reply to Consumer unit change - How do you do it? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
446
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
793

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top