Consumer unit change testing | on ElectriciansForums

Discuss Consumer unit change testing in the UK Electrical Forum area at ElectriciansForums.net

Joined
Nov 25, 2016
Messages
18
Reaction score
5
Location
Norwich
hi all I've got my first consumer unit change to do as I'm using this as my first nic assessment. My question is when doing my ir test the whole house is on led downlights about 30 of then plus under kitchen 12v led and a lot of sub sockets, will all,of theses need to be disconnected to do these test. Also do I need to do r1+r2 on every downlight.

Any advice is much appreciated as this is my first nic assessment after this change.

Thanks
 
I can see why you would ask that I just don't want to mess anything up as I haven't done the ir test this way before it just so happens this house has a lot of LEDs and sub sockets in and would take ages to go round and take everything out then put back in. So I would rather check first as this way will save a lot of time.
 
As above. Tie L & N together and IR test between that and earth.
If you are really unsure, wind your IR tester down to 250VDC for the test. No need to go for 500V if the test results at 250 are OK.
 
As above. Tie L & N together and IR test between that and earth.
If you are really unsure, wind your IR tester down to 250VDC for the test. No need to go for 500V if the test results at 250 are OK.
500v is the required voltage.
 
I would measure R1 + R2 at each light fitting. How is he proving continuity of protective conductors by only testing at the final light fitting?

If there was a break in the earth conductor prior to the final light, he wouldn't be able to get the reading as there would be no earth path back to CU.

I rarely bother with R1+R2, usually Zs-Ze although i feel thats a brave statement on this forum
 
I would measure R1 + R2 at each light fitting. How is he proving continuity of protective conductors by only testing at the final light fitting?
House with, say, 100+ recessed downlights and you're going to pull each one out of the ceiling. Pull the other one.
 

Reply to Consumer unit change testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
282
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
792

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top